Discuss Distribution circuits in apartment block Electrical Advice in the Electrical Advice area at TilersForums.com.

Distribution circuits in apartment block Discussion ThreadDistribution circuits in apartment block Electrical Advice

Hi all,

First time poster here, albeit long time lurker.

I could do with some opinions on running distribution circuits around and through the building voids of an apartment block. The project is an old police station being converted into flats. The bloke from the private DNO approved company came out today to discuss getting a new main into the building. The building layout is such that there are 3 different communal hallways and one lobby area that was being reserved as a plant room to install all the meters. This lobby area is not directly accessible to two of the communal hallways.

In other words, the distribution circuits from kmf to comsumer unit would have to run above mf ceilings for other flats to get to the destination flat. Hope that makes sense.

The DNO bloke is saying that he can't put one big ryefield in the lobby because that would mean running power through a flat that it's not intended for. He's suggesting make multiple connections in the street and bring power into the building in multiple locations at great cost for the owner.

Just to be clear, this is NOT a BNO installation, it would be ryefield - red link cut out - meter - metclad kmf - swa to consumer unit. So it would be us installing the everything downstream of the meter and would therefore fall under BS7671.

As far as I'm aware, there is nothing in BS7671 prohibiting running a supply for one flat through another and I believe we would be ok for building regs as long as there is proper fire stopping etc..

So, my question, is there anything I have overlooked or just got plain wrong? No idea why the DNO would have any concern about our installation tbh, it's not really anything to do with him but I don't want to start arguing the ---- and then realise I was wrong. Any thoughts are more than welcome.

Thanks, DS1982

Distribution circuits in apartment block for the original thread on Electricians Forums
 

Reply to Distribution circuits in apartment block Electrical Advice in the Electrical Advice area at TilersForums.com

Subscribe to Tilers Forums

Advertisement

Thread starter

Lou

Staff member
Admin
Joined
Location
Staffordshire
Website
https://www.TilersForums.com
What member type are you?
  1. Support Rep (here to provide support only)
Business Name
TilersForums.com

Thread Information

Title
Distribution circuits in apartment block Electrical Advice
Prefix
N/A
Forum
Electrical Advice
Start date
Last reply date
Replies
0

Thread Tags

Tags
None

Which tile adhesive brand did you use most this year?

  • Palace

    Votes: 9 6.0%
  • Kerakoll

    Votes: 14 9.3%
  • Ardex

    Votes: 11 7.3%
  • Mapei

    Votes: 44 29.1%
  • Ultra Tile

    Votes: 18 11.9%
  • BAL

    Votes: 36 23.8%
  • Wedi

    Votes: 3 2.0%
  • Benfer

    Votes: 2 1.3%
  • Tilemaster

    Votes: 21 13.9%
  • Weber

    Votes: 18 11.9%
  • Other (any other brand not listed)

    Votes: 16 10.6%
  • Nicobond

    Votes: 7 4.6%
  • Norcros

    Votes: 3 2.0%
  • Kelmore

    Votes: 4 2.6%
Top