Discuss Minor works - Zdb & R1R2 tests Electrical Advice in the Electrical Advice area at TilersForums.com.

Minor works - Zdb & R1R2 tests Discussion ThreadMinor works - Zdb & R1R2 tests Electrical Advice

Hi all, when completing a minor works there are two tests that i am unsure the best way to go about, example extension of circuit and new lighting point installed. Fed from industrial 3P board unable to isolate due to plant running. Do not wish to open live board even just for testing purposes for safety reasons. ( don't want to be putting hands in there with single insulated cables etc and some board are very old )

All other tests can be completed its just the Zdb and R1R2

  1. Could Zdb be took from enquiry ( a recent ECIR ) ?
  2. Can R1R2 be calculated from ZS minus ZDB? Leave a note measuring r1r2 on just the new length of cable installed only as this can be completed dead.
  3. Tick box on part 2 - Presence of adequate main protective conductor? - Is the only way to tick this to remove the cover and visually check?

Would this be acceptable?

Minor works - Zdb & R1R2 tests for the original thread on Electricians Forums
 

Reply to Minor works - Zdb & R1R2 tests Electrical Advice in the Electrical Advice area at TilersForums.com

Subscribe to Tilers Forums

Advertisement

Thread starter

Lou

Staff member
Admin
Joined
Location
Staffordshire
Website
https://www.TilersForums.com
What member type are you?
  1. Support Rep (here to provide support only)
Business Name
TilersForums.com

Thread Information

Title
Minor works - Zdb & R1R2 tests Electrical Advice
Prefix
N/A
Forum
Electrical Advice
Start date
Last reply date
Replies
0

Thread Tags

Tags
None

Which tile adhesive brand did you use most this year?

  • Palace

    Votes: 9 6.0%
  • Kerakoll

    Votes: 14 9.3%
  • Ardex

    Votes: 11 7.3%
  • Mapei

    Votes: 44 29.3%
  • Ultra Tile

    Votes: 17 11.3%
  • BAL

    Votes: 36 24.0%
  • Wedi

    Votes: 3 2.0%
  • Benfer

    Votes: 2 1.3%
  • Tilemaster

    Votes: 21 14.0%
  • Weber

    Votes: 18 12.0%
  • Other (any other brand not listed)

    Votes: 16 10.7%
  • Nicobond

    Votes: 7 4.7%
  • Norcros

    Votes: 3 2.0%
  • Kelmore

    Votes: 4 2.7%
Top