bluesky
went to deliver tiles of a job i`m starting on monday to discover that the builders have decided to lay screed over the top of electric cables 30mm thick .this was instead of laying 20 mm insulation board then cable then latex to build up to the correct height . they have told my customer that it will all be dry in time for monday as they have added pva to the mix! normally i would allow minimum of 3 weeks for this screed to dry but also i am concerned about the heating up times and costs .normally latex will only cover the cables my 2-3 mm.if i am correct with regards to screed not being dry could i get round this by using ditra.?
many thanks for any input.
Spud
tyco have got an electric ufh cable that can be screeded over with sand and cement but that 30mm screed wont be ready for tiling on monday and i am not sure why they put pva through it, with wet system ufh its normally a 60mm fibre screed that is used so i would be a bit wary of future problems unless they can show you some technical data to back up their preparation method
Ajax123
1,213
Lincolnshire
One assumes that the conrete slab was not mechanically prepared - it would be very un usual to see this done to say the least. BS8204 treats this as an unbonded screed although the industry terms it partially bonded. This means that the minimum depth should have been 50mm. 30mm is simply too thin for sand cement and there is a real risk that the screed will crack when subjected to heating. Additionally if the concrete underneath is new this can take an age to dry properly (100mm concrete takes in excess of 12 months to dry) so the residual moisture in the concrete will want to rise through the screed. Additionally PVA degrades when in the presence of alkalis (cement is alkaline) so over a period of time the screed will potentially begin to fail although this is relatively low risk and not something you as the tiler need really worry too much about.:thumbsdown:
The best idea would have been to use an anhydrite screed at this depth if they had to screed it but I cannot think why they did not go with the original plan except to cut costs cos insulation would have been more expensive than the screed at this depth. The other problem of course is that the efficiency of the underfloor heating will be seriously impaired cos they will now be trying to heat up the entire slab and not just the screed. This one is a deffinite candidate for an uncoupling mat in my opinion.
Why can't people just build things properly!!:incazzato:
Ajax123
1,213
Lincolnshire
am i correct then with drying time of 21 days for the 30mm screed then use ditra mat with spf ?
3 weeks will get you somewhere near dry I would think. On the basis of the risks previously explained I would certainly not be entertaining this one without uncoupling
Ajax123
1,213
Lincolnshire
dear bluesky you need to leave an (opc) mixed screed three weeks to cure (not dry out) its a chemical reaction according to BS standards if your installation fails you are open to litigation:oops: POSTPONE MATE GOONER 59
Curing is where the moisture is trapped within the screed in order to promote the hydration reaction betwee the cement and the water. It is a separate aspect to drying. According to BS8204 sand cement screeds should be cured by covering with a sheet of polythene for a period not less than 7 days following instalation in order for the screed to go hard. Once cured the screed can then be dried. This is the process by which surplus residual moisture is removed from the screed by evaporation in order to equilibrate the moisture in the screed with the moisture in the atmosphere. If the two are not equillibrated then the vapour pressure in the screed being higher than that in the atmosphere (normally accepted as 75% although this includes a 5% testing error) then the upward movement of the residual moisture can cause a failure of the bond between the adhesive and the screed. This is for two reasons, firstly the primer (usually acrylic or SBR ) will soften and reduce the mechanical bond between it and the interface. Secondly the excess moitsure can cause the adhesive to soften again causing a failure. This is when he tiles delaminate. WIth anydrites there is a third mechanism in place and that is the chemical interaction between the cement in the adhesive and the sulphates in the screed which promoes the formation of Ettirgnite and Thaumesite sulphate salts which disrupt the bond again causing delamination. Ditra is one way to prevent this bit but there are other methods as well.
A fully compacted 1:4 sand ceent screed will have a dring rate of around 1mm per day. Trapping moisture on a screed based on portland cement is not detrimental to the screed as the hydration reaction will continue ad infinitum whilst there s moisture present. The Ditra acts as a vapour equalisation layer thus equilibrium with the atmosphere is not necessary and as grumpy rightly says it can be placed as soon as the screed is hard enough to walk on. It does not matter if it becomes delaminated lightly because the tiles are completely divorced from the screed.:thumbsup:
Reply to screed instead of latex in the British & UK Tiling Forum area at TilersForums.com
gamer1
Hello Folks, I need to sort my floor out before I can lay tiles on it so seeking advice from...
Hi I am posting in the hope that someone may be willing to offer me some advice about floor...
    Votes: 14 9.4%
    Votes: 44 29.5%
    Votes: 17 11.4%
    Votes: 35 23.5%
    Votes: 21 14.1%
    Votes: 18 12.1%
    Votes: 16 10.7%