Hello
45mm Anhydrite screed (Aggregate Industries 'Highflow') is now dry (moisture tested by contractor). Thoroughly dried out with 2 x dehumidifiers running 24x7 for 45 days. Wet UFH system in screed - but boiler is not yet installed - so can't take the floor through a thermal stress cycle. Will be tiling using slate 10-12mm thick various sizes from 300x300mm up to 1200x900mm. Using Tilemaster Primeplus for sealing/bonding. Using S2 adhesive for max flex - 10mm square notch + buttering. Any views on whether it is really necessary to hire in a temp boiler to take the floor through a thermal shock cycle before tiling?
Many thanks, Andy
 
Some more info - trying to answer my own question after speaking to a few people. My approach: keep asking Why? (which is what small children do continuously)

Why does the floor need to be commissioned before tiling?

1. pressure test for integrity of UFH pipework - done and PASS
2. to expel moisture - done & PASS (Calcium Carbide test - the best method)
BUT the method for dying the screed according to the supplier does not require the floor to be heated - instead, forced drying using UFH is listed as an option (see attached)
3. for structural integrity / movement
BUT it isn't going to move much - coefficient of thermal expansion: ≤ 0.01 mm/m/°C (see attached) - flexible tile adhesives should more than cope with this. So taking the floor through a thermal cycle for structural / movement reasons before tiling would seem to serve no purpose.

So why might tiling fail on an Anhydrite screed?

1. screed not dry enough - done and PASS
2. surface prep / laitance not removed - done
3. cementitious adhesive used without a primer / sealer - will use Primeplus
4. poor installation - will be done properly
5. future substrate movement - low risk as insulation acts as a decoupling layer between slab and screed

So back to the original question: Why heat the floor prior to tiling?
The only reason I can see relates to moisture / drying - and the main reason for doing it seems to be to speed up the drying process - but it still needs to be tested and it's the test result which gives the green light for the next stage.

Does anyone agree / disagree?
 

Attachments

  • Highflow S Drying Guidelines v4.pdf
    259.9 KB · Views: 36
  • screed-free-flowing-highflow-tds.pdf
    281.4 KB · Views: 41

Ajax123

TF
Esteemed
Arms
932
1,213
Lincolnshire
Some more info - trying to answer my own question after speaking to a few people. My approach: keep asking Why? (which is what small children do continuously)

Why does the floor need to be commissioned before tiling?

1. pressure test for integrity of UFH pipework - done and PASS
2. to expel moisture - done & PASS (Calcium Carbide test - the best method)
BUT the method for dying the screed according to the supplier does not require the floor to be heated - instead, forced drying using UFH is listed as an option (see attached)
3. for structural integrity / movement
BUT it isn't going to move much - coefficient of thermal expansion: ≤ 0.01 mm/m/°C (see attached) - flexible tile adhesives should more than cope with this. So taking the floor through a thermal cycle for structural / movement reasons before tiling would seem to serve no purpose.

So why might tiling fail on an Anhydrite screed?

1. screed not dry enough - done and PASS
2. surface prep / laitance not removed - done
3. cementitious adhesive used without a primer / sealer - will use Primeplus *use anhyfix instead of cement based adhesive.
4. poor installation - will be done properly *if I had a pound for every failed installation that had been done "properly"
5. future substrate movement - low risk as insulation acts as a decoupling layer between slab and screed *not relevant as screed is acted on by thermal cycling not sub slab

So back to the original question: Why heat the floor prior to tiling?
The only reason I can see relates to moisture / drying - and the main reason for doing it seems to be to speed up the drying process - but it still needs to be tested and it's the test result which gives the green light for the next stage.

Does anyone agree / disagree? *yes
Ive added a couple of asterisked notes to your research

There are 2 primary reasons for commissioning the underfloor heating with any screed. The first is that it helps to force dry the screed. The second and much more importantly, when you turn on the heating you will cause the screed to expand.This is when it is vulnerable to restraint cracking. As it then subsequently cools it contracts. This is when it is vulnerable to shrinkage and further restraint cracking. If you have stuck your expensive slate tiles down they will crack with the screed. Further, the slate and adhesive and screed expand at different rates therefore further stress is applied to the interfaces which can also cause localised failures either cracking or full depending due to tenting. Thus is especially risky if using a cement based adhesive. Bear in mind also that the primer and the adhesive add water to the system so it'll be damp hence use anhyfix instead of cement based adhesive to avoid chemical reaction with the screed.

If it does crack before you tile you can repair the cracks and move forward more easily. If you tile first and it cracks you will want to blame someone but you'll not have much of a claim as you have gone against tule manufacturers advice, British Standards, TTA best practice, the stone federation advice and the recommendation of any knowledgeable tiler, screed installer, underfloor heating designer and screed manufacturer

You are using natural stone on a heated screed. The recommendation of the stone federation us that a decoupling mat should be used.

All that said...you have done your own research although some of your conclusions are flawed. You can do whatever you like. Its your floor, your tiles, your money...
 
Really helpful advice - thanks so much Ajax & Dave. One reason I'm tying to really understand this is because this sits between 3 trades: i) screed manufacturer/installer, ii) UFH designer/installer and iii) tiling/tile installer - and I'm getting conflicting views. So I'm back to basics - keep asking why!
I wonder if any prof tilers have actually experienced a screed cracking due to being heated up and then needing repair before tiling?
 

Dave

TF
Staff member
Esteemed
Arms
Subscribed
389,925
1,000,000
Co.Durham
Really helpful advice - thanks so much Ajax & Dave. One reason I'm tying to really understand this is because this sits between 3 trades: i) screed manufacturer/installer, ii) UFH designer/installer and iii) tiling/tile installer - and I'm getting conflicting views. So I'm back to basics - keep asking why!
I wonder if any prof tilers have actually experienced a screed cracking due to being heated up and then needing repair before tiling?
I have yes , screed was crack free prior to commencing heating. Then cracking occurred in 3 places. No tiler worth his salt will tile before a screed has been commissioned.
 
Dave, thanks. For your example, had the floor properly dried out before commencing heating? - or were they force-drying?

A bit more context for my situation ...

I can't heat the floor because I don't yet have the UFH boiler installed - that is months away and we need a functional floor ASAP. If I had the ability to heat the floor - there is no question about doing that - I would take the floor through several thermal cycles. I also do not question stone fed, TTA etc guidance and best practice.
The cost of hiring in a temp set up to heat the floor is significant (£ hundreds + time - hassle). So I am trying to do a cost-benefit assessment.
Another factor to consider is that the slate tiles will be randomly placed - so there are no straight-line grout lines. Also slate is one of the strongest natural stones and is resistant to cracks, etc.
 

Ajax123

TF
Esteemed
Arms
932
1,213
Lincolnshire
Really helpful advice - thanks so much Ajax & Dave. One reason I'm tying to really understand this is because this sits between 3 trades: i) screed manufacturer/installer, ii) UFH designer/installer and iii) tiling/tile installer - and I'm getting conflicting views. So I'm back to basics - keep asking why!
I wonder if any prof tilers have actually experienced a screed cracking due to being heated up and then needing repair before tiling?
It sits between 3 trades but you are the main contractor/client so you carry ultimate responsibility. You are also the one who is paying so if it goes wrong you will be the one who ultimately picks up the bill. I'm not sure what you are trying but failing to understand. Conflicting views on what... conflicting views on the requirements of the standards...that comes down to the level of expertise that individuals have. I personally gave a fair degree of experience with these screeds. I'm asked the same question a lot... the answer... see my previous post.

That your boiler is not available would not constitute a defence in any civil action you might take if the floor fails. You can just hire a temporary boiler... job done.

As I said you can do whatever you like. You may get lucky you may not... it's a lottery regardless but if you follow the rules it mitigates risk. We dont make recommendations for the sake of it.
 

Ajax123

TF
Esteemed
Arms
932
1,213
Lincolnshire
Dave, thanks. For your example, had the floor properly dried out before commencing heating? - or were they force-drying?

A bit more context for my situation ...

I can't heat the floor because I don't yet have the UFH boiler installed - that is months away and we need a functional floor ASAP. If I had the ability to heat the floor - there is no question about doing that - I would take the floor through several thermal cycles. I also do not question stone fed, TTA etc guidance and best practice.
The cost of hiring in a temp set up to heat the floor is significant (£ hundreds + time - hassle). So I am trying to do a cost-benefit assessment.
Another factor to consider is that the slate tiles will be randomly placed - so there are no straight-line grout lines. Also slate is one of the strongest natural stones and is resistant to cracks, etc.
You seem to be fishing for answers that dont exist. You clearly have it in mind to ignore the advice so I'd suggest you just get on with it. You'll not get anyone to say " yes...good idea bat man, you clearly know your stuff better than the experts" unless in a sarcastic manner.

It's not a cost vs benefit exercise, it's a lottery. Up to you. Pay your money make your choice.
 
Last edited:

Dave

TF
Staff member
Esteemed
Arms
Subscribed
389,925
1,000,000
Co.Durham
Dave, thanks. For your example, had the floor properly dried out before commencing heating? - or were they force-drying?

A bit more context for my situation ...

I can't heat the floor because I don't yet have the UFH boiler installed - that is months away and we need a functional floor ASAP. If I had the ability to heat the floor - there is no question about doing that - I would take the floor through several thermal cycles. I also do not question stone fed, TTA etc guidance and best practice.
The cost of hiring in a temp set up to heat the floor is significant (£ hundreds + time - hassle). So I am trying to do a cost-benefit assessment.
Another factor to consider is that the slate tiles will be randomly placed - so there are no straight-line grout lines. Also slate is one of the strongest natural stones and is resistant to cracks, etc.
Its not the cracks etc. It’s the de-bonding , listen your talking yourself into an installation without the correct procedures. We can only advise. Good luck and report back when it fails.
 
So some feedback from the bat cave: the decision is to go for a thermal shock using a hired-in boiler. Screed supplier is suggesting 7 day shock cycle given that no additioinal time is required for drying (usually the boiler would be hired out for a 3 week period). Thanks again for all the advice - much appreciated.
 

Reply to Slate over Anhydrite screed - commissioning a in the America Tile Forum / Advice Board area at TilersForums.com

Subscribe to Tilers Forums

There are similar tiling threads here

I've had a look through threads but cannot find anything on this. Lots of info on commissioning...
Replies
1
Views
130
I am planning to lay 600mm x 600mm x 20mm slate on to an anhydrite screed. It is a very thick...
Replies
0
Views
3K
Just seen Rocatex on uHeat.co.uk and thought hmmm that's a new one on me. Anybody used it yet...
Replies
3
Views
2K
Hi i'm self building my own barn conversion and have a anhydrite screed and underfloor heating...
Replies
4
Views
2K
H
We had a 50mm anhydrite screed down over a DPM around 100 days ago. For the first 50 days the...
Replies
18
Views
19K
Spacey
S

USA Tile Forum Popular

America Tile Advice Trending

Advertisement

Thread starter

Joined
Location
Callington
What member type are you?
  1. Homeowner
  2. DIY Wall and Floor Tiler
Business Name
Living Works

Thread Information

Title
Slate over Anhydrite screed - commissioning a
Prefix
N/A
Forum
America Tile Forum / Advice Board
Start date
Last reply date
Replies
15

Which tile adhesive brand did you use most this year?

  • Palace

    Votes: 5 4.3%
  • Kerakoll

    Votes: 10 8.5%
  • Ardex

    Votes: 7 6.0%
  • Mapei

    Votes: 32 27.4%
  • Ultra Tile

    Votes: 15 12.8%
  • BAL

    Votes: 31 26.5%
  • Wedi

    Votes: 3 2.6%
  • Benfer

    Votes: 2 1.7%
  • Tilemaster

    Votes: 19 16.2%
  • Weber

    Votes: 18 15.4%
  • Other (any other brand not listed)

    Votes: 13 11.1%
  • Nicobond

    Votes: 5 4.3%
  • Norcros

    Votes: 3 2.6%
  • Kelmore

    Votes: 2 1.7%
Top