Testing the SELV Discussion ThreadTesting the SELV Electrical Advice

Correct me if I am wrong but if we are to test a SELV transformer do we:

1. Join conductors of low voltage side of transformer together.
2. Join conductors of primary side of transformer together.
3. Test between these at a voltage of 500V look for minimum reading of 1 MOhm.
4. Test between joined conductors of low voltage side and the earth of the primary side at 500V Look for minimum of 1MOhm.
5. Test between conductors of low voltage side at 250V look for minimum reading of 0.5 MOhm.

When testing the conductors on the low voltage side at 250V this is including the transformer winding right?
I mean is this low 250V test a test of insulation resistance of cables but also including the resistance of the winding inside the transformer.
Is that right?
Thanks.

Testing the SELV for the original thread on Electricians Forums
 

Reply to Testing the SELV Electrical Advice in the Electrical Advice area at TilersForums.com

Please visit our sponsor websites, they keep the forum free to use!

Advertisement

Thread starter

Lou

Staff member
Esteemed
Admin
Joined
Location
Staffordshire
Website
https://www.TilersForums.com
What member type are you?
  1. Support Rep (here to provide support only)
Business Name
TilersForums.com

Thread Information

Title
Testing the SELV Electrical Advice
Prefix
N/A
Forum
Electrical Advice
Start date
Last reply date
Replies
0

Thread Tags

Tags
None

Which tile adhesive brand did you use most this year?

  • Palace

  • Kerakoll

  • Ardex

  • Mapei

  • Ultra Tile

  • BAL

  • Wedi

  • Benfer

  • Tilemaster

  • Weber

  • Other (any other brand not listed)

  • Nicobond

  • Norcros


Results are only viewable after voting.
Top