Hi lads, customer has a new build with standard concrete floor which has been down for 4 months (no problem) they have also got underfloor heating, (hot water pipe system) the screed on top of water pipes has only been layed for 4 weeks and they are phoning me all the time saying it is ready for tiling, i have explained to them that the floor will take 2 months to dry and ready for tiling (especially this time of the year) otherwise the floor tiles could crack with any hidded moisture, i understand that they are keen to get the job finished but i would walk away from the job rather than them pressureize me into starting too soon. What's your views on this??? thank's in advance for any replies.
 
N

nalla

1) Has the UFH been commissioned ?
2) How thick is the screed?
3) You could use a decoupling membrane to hasten the process.
The ufh has not been commissioned because it is a free standing water tank which will be on top of the floor tiles, as for the thickness of the screed i don't really know because i was on another job when they had it laid, i will ask them for the builders number and ask him myself but they told me it was the standard thickness for the job.
 

Sean Kelly

TF
Arms
647
1,068
Ruislip
Nalla, the guidelines for screed and wet UFH are:
Lay screed and wait at least 3 weeks for movement and shrinkage.
Switch on UFH at a rate of 5degs every 24 hours upto max operating temp.
Maintain max temp for 3 days then turn off.
Wait 48 hours then tile.

However, if you are using a natural stone tile then use Ditra.
If using Porcelain then it should be fine to tile without Ditra.

Before you do the above, I suggest you find a plastic bucket or a sheet of plastic with a tile on top and place it on the floor for 24 hours. If after 24 hours there is moisture then it is not safe to do any of the above.

I went to a house just before Xmas and the owners said the screed was dry. I put a plastic paint tub on the floor and picked it up 15mins later. There was a wet patch on the screed in the shape of the bottom of the bucket!
 
N

nalla

Ok you need to know the thickness of the screed and allow 1mm per day for drying from day of drop.
Unless the UFH has been commissioned I wouldn’t lay any tiles without a decoupling membrane.
Has the UFH been pressure tested?
I've been in touch with the person who laid the screed and he told me that the screed he used goes off in two weeks and on average is 75mm thick, the ufh has been pressure tested so i,ve told the customer that i,ll return on the 19th february and take it from there.
 
N

nalla

Nalla, the guidelines for screed and wet UFH are:
Lay screed and wait at least 3 weeks for movement and shrinkage.
Switch on UFH at a rate of 5degs every 24 hours upto max operating temp.
Maintain max temp for 3 days then turn off.
Wait 48 hours then tile.

However, if you are using a natural stone tile then use Ditra.
If using Porcelain then it should be fine to tile without Ditra.

Before you do the above, I suggest you find a plastic bucket or a sheet of plastic with a tile on top and place it on the floor for 24 hours. If after 24 hours there is moisture then it is not safe to do any of the above.

I went to a house just before Xmas and the owners said the screed was dry. I put a plastic paint tub on the floor and picked it up 15mins later. There was a wet patch on the screed in the shape of the bottom of the bucket!
The tiles are natural stone, after primming i was going to lay them directly on to the screed as they are with RSF (weber)
 

Ttt1601

TF
Esteemed
Arms
I had a similqr problem to this not so long ago in regards to ufh not being commission ed as the tank and boiler were not going to be fitted until last to the air recirculation system and some other stuff, had a good chat with the main contractor, who is a good mate of mine and a plumber buy trade, we came up with the solution of using an electric water heater, all be it a fairly large one, with the ufh system full, he did what he had to to get the electric heater running the ufh, so manged to fully commissioned first
 
D

Dumbo

I had a similqr problem to this not so long ago in regards to ufh not being commission ed as the tank and boiler were not going to be fitted until last to the air recirculation system and some other stuff, had a good chat with the main contractor, who is a good mate of mine and a plumber buy trade, we came up with the solution of using an electric water heater, all be it a fairly large one, with the ufh system full, he did what he had to to get the electric heater running the ufh, so manged to fully commissioned first
Apparently there is a builder round our called Ray Ferguson who does this as a matter of course.
 
J

Just Rizzle

you need to
a) take a moisture reading to ensure floor is dry.
b)lay a decoupling mat as sand and cement screed will expand and contract and the floor will crack so will the tiles if laid directly on to the screed
c)it would be prefered to commission the ufh but if you have it under preasure to at least 3bar and remaining on during the laying you should be ok
 
N

nalla

This job is not going to end well if you stick the stone to this screed after only 6 weeks with no ufh commissioning and no uncoupling.
I would insist on commissioning the ufh, then fit durabase mat or ditra to control the moisture which is left
I've sorted it now, i told him politely to get back the builder who laid the screed to lay the tiles as i wasn't prepared to lay them until the UFH had been running for at least a week, the customer insists that the floor is now ready for the tiles (it,s only been down for 3 weeks) where as i told him i would come back at the end of february, (26th) i also told him not toring me back in 6 months time when the tiles will have cracked. Thanks lads for all the replies it makes my choice feel that much easier.
 

Ttt1601

TF
Esteemed
Arms
Apparently there is a builder round our called Ray Ferguson who does this as a matter of course.

I've heard of ray, never done any work for him tho, don't see the point of rigging up the electric system if the boiler can be fired? We just thought of it because it was impossible to get the boiler in for a couple months, and my tiles had to go down before aga, kitchen, water tank etc etc
 
This thread hasn't been replied to for 14 days, so replying to this one may not get a response. Post a new thread instead.

Reply to TILING ON CONCRETE SCREED in the Canada Tile Advice area at TilersForums.com

There are similar tiling threads here

    • Like
Hi guys. Im a carpenter who has tiled a fair few floors over the years as i fit a lot of...
Replies
13
Views
1K
Hi - I ripped up laminate flooring on a concrete subfloor. It was my first DIY project and...
Replies
2
Views
540
I had a small leak in the main water line before the stop tap in my 1950s house. The copper pipe...
Replies
1
Views
1K
    • Like
Renovated the bathroom on my 1970 bungalow last year. Took up the old pink floor tiles with sds...
Replies
24
Views
2K
    • Like
Hi everyone I am building my own house and now I'm ready to tile the floor downstairs. I have...
Replies
1
Views
897

Advertisement

Tilers Forums on FB

...
Top