Sadly the presence of laitance on anhydrite screed preventing drying is also a myth. It was disproved some 3 or 4 years ago in some independent testing that was done. the testing looked at drying anhydrite screeds specifically in both normal and force dried scenarios. It was demonstrated that removal of laitance made no difference at all. It also looked at drying in comparison to that of sand and cement screeds and found that they dried at almost exactly the same rate per mm of depth.were sanding to allow the hard layer on the surface to be removed as this will allow drying to happen quicker were running 4 big fans 24hrs a day to circulate the air so allowing drying faster.
the hard surface layer slows down drying as it helps retain the moisture.
no evidence to show it dos not either. but air circulation dose
Air circulation most definitely improves drying of all screeds. As does increasing the temperature eg with UFH. Temperature though is almost irrelevant if there is no ventilation as theres no where for the moisture to go.