Calcium sulphate screedforms a perfect compliment for an underfloor heating system being suitable for use with both wet systems and electric systems. The nominal septh of traditional screed over underfloor heating would be 75mm (yes I know sometimes it is laid thinner) with anhydrite you are able to reduce the depth of the sacreed significantly to just 25mm to meet BS8204 part 7 and 30mm to meet the requirements outlined by most manufacturers. This offers a number of advantages with heated screeds but before we look at them let us look at the standard design requirements and some of the possible pitfalls.
1. It is very important that the screed is divorced from the substrate by means of a Damp Proof Membrane, usually a 1200 gauge polythene over the substrate. It is common to see this folded up the walls behind the edge strip but in my opinion this is un-necessary as there should be a damp proof membrane under the concrete which serves to protect the srtucture. provided the screed does not bridge this then the DPM over the concrete can just be cut almost flush to the walls as it is only there to prevent the residual substrate moisture from rising through the floor and extending the screed drying time. I also see a lot of installations where the DPM has been moved upward on the zone ot on top of the insulation. This is a bad idea if you are using underfloor heating pipe clips to secure the pipes as these will clearly then breach the DPM so it becomes a seive instead.
2. The screed depth should be designed to meet as close to the minimum as possible. I see a lot of designs where the insulation is designed to meet the u-value required and then the screed placed to make up the zone. What would be better would be to design the insulation depth based on the minimum depth of screed (normally 50mm nominal). placing the screed too deeply results in significantly extended drying times.
3. The screed should not be placed at belos the nominal inimum design depth as this can lead to overheating at the surface of the screed and the posibility of pipe mapping and plastic settlement cracking over the pipes.
The screed should be designed with consideration for expansion and contraction. Whilst it is much more dimensionally stable than traditional materials it should still be joined across all door thresholds and where there are abrupt or significant changes to aspect ratio or direction. Joints should also be placed at the interface between independently controlled heating zones, remembering that generally there will be up to 8 curcuits within the same zone. All of these joints should be formed using a full depth isolating former ideall of a compressible material and should be between 5mm an 12mm wide. All joints should be fully reflected through the tiled surface. Remember uncoupling membranes are not designed to replace joints.
Now to look at some of the benefits. The screed has a very high thermal conductivity at around 2.2W/mK. The fact that the screed is fully self compacting means that there are no air pockets trapped within the screed which would lead to a less efficient heat transfer. Additionally the screed flows freely and completely around the heating pipes to offer a full contact surface for the heat transfer. The material is laid thinner so that there is less material to physically heat up. All of leads to greater efficiencies in the heating system meaning effectively that to get the same heat output compared to traditonal materials you need put less energy in. This makes anhydrite perfect for use with geo thermal heating systems as well as other more traditonal systems. It allows trhe screed to act more like a radiator than a storeage heater.
The fact that it can be laid thinner than traditional materials means that the design of the insulation can be considered in a more flexible way. For example if there is no desire or no possibility to alter the depth of the overall floor zone we can look to change the depth of the insulation. This allows the use of potentially more environmentally freindly insulations to meet or exceed the required U Value. When the U-Value is calculated using for example a poly urethane insulation having a r value of 0.023 at say 75mm I can look at changing the insulation type to an EPS100 polystyrene at 100mm with an R aValue of 0.030 and generally exceed the u-value we achieved using the PU. this would offer a cost saving in most instances. Alternatively and possibly more desirably in many smaller installations we can simply increase the depth of the insulation to enhance the u-value significantly and make the floor more environmentally freindly and in the long term cheaper to run.
The alternative of course it to physically reduce the depth of the floor zone although this can generally only be acheived at design stage because once the build gets past ground floor level it is too late. In this instance though reducing the screed depth by 25mm meansd that less material is used in the overall construction. This would often not suit traditional masonry construction where floors are usually designed to fit in with brick coursing. Where it can be done though the reduction in material use leads to lower levels of emboddied energy in the whole construction. I have seen instances particularly where the timber frame systems have been used where an entire course of bricks per floor has been removed with very significant material cost savings to the builder as well. The possible reduction in floor zone is up to 35mm.
Where electrical underfloor heating systems are used it important that the cables are controlled by means of floor stats instead or as well as room stats as there can be a risk of the floor overheating.
Turning the general floor temperature down not only leads to energy savings but also reduces the risks associated with thermal expansion and contraction of the screed and the inpact this has on the finished floor coverings.
The temperature of the underfloor heating system should not exceed 55oC for anhydrite during the comissioning phase and it is generally recomended that this is limited to 45oC during the operation of the floor. This would normally lead to a surface temeprature which is comfortable.
The surface of the screed in operation should feel at best slightly warm to the touch based ont he temerature differential of this (maximum 27oC) and the temperature of the average human hand. If the floor feels hot it is generally too hot.
1. It is very important that the screed is divorced from the substrate by means of a Damp Proof Membrane, usually a 1200 gauge polythene over the substrate. It is common to see this folded up the walls behind the edge strip but in my opinion this is un-necessary as there should be a damp proof membrane under the concrete which serves to protect the srtucture. provided the screed does not bridge this then the DPM over the concrete can just be cut almost flush to the walls as it is only there to prevent the residual substrate moisture from rising through the floor and extending the screed drying time. I also see a lot of installations where the DPM has been moved upward on the zone ot on top of the insulation. This is a bad idea if you are using underfloor heating pipe clips to secure the pipes as these will clearly then breach the DPM so it becomes a seive instead.
2. The screed depth should be designed to meet as close to the minimum as possible. I see a lot of designs where the insulation is designed to meet the u-value required and then the screed placed to make up the zone. What would be better would be to design the insulation depth based on the minimum depth of screed (normally 50mm nominal). placing the screed too deeply results in significantly extended drying times.
3. The screed should not be placed at belos the nominal inimum design depth as this can lead to overheating at the surface of the screed and the posibility of pipe mapping and plastic settlement cracking over the pipes.
The screed should be designed with consideration for expansion and contraction. Whilst it is much more dimensionally stable than traditional materials it should still be joined across all door thresholds and where there are abrupt or significant changes to aspect ratio or direction. Joints should also be placed at the interface between independently controlled heating zones, remembering that generally there will be up to 8 curcuits within the same zone. All of these joints should be formed using a full depth isolating former ideall of a compressible material and should be between 5mm an 12mm wide. All joints should be fully reflected through the tiled surface. Remember uncoupling membranes are not designed to replace joints.
Now to look at some of the benefits. The screed has a very high thermal conductivity at around 2.2W/mK. The fact that the screed is fully self compacting means that there are no air pockets trapped within the screed which would lead to a less efficient heat transfer. Additionally the screed flows freely and completely around the heating pipes to offer a full contact surface for the heat transfer. The material is laid thinner so that there is less material to physically heat up. All of leads to greater efficiencies in the heating system meaning effectively that to get the same heat output compared to traditonal materials you need put less energy in. This makes anhydrite perfect for use with geo thermal heating systems as well as other more traditonal systems. It allows trhe screed to act more like a radiator than a storeage heater.
The fact that it can be laid thinner than traditional materials means that the design of the insulation can be considered in a more flexible way. For example if there is no desire or no possibility to alter the depth of the overall floor zone we can look to change the depth of the insulation. This allows the use of potentially more environmentally freindly insulations to meet or exceed the required U Value. When the U-Value is calculated using for example a poly urethane insulation having a r value of 0.023 at say 75mm I can look at changing the insulation type to an EPS100 polystyrene at 100mm with an R aValue of 0.030 and generally exceed the u-value we achieved using the PU. this would offer a cost saving in most instances. Alternatively and possibly more desirably in many smaller installations we can simply increase the depth of the insulation to enhance the u-value significantly and make the floor more environmentally freindly and in the long term cheaper to run.
The alternative of course it to physically reduce the depth of the floor zone although this can generally only be acheived at design stage because once the build gets past ground floor level it is too late. In this instance though reducing the screed depth by 25mm meansd that less material is used in the overall construction. This would often not suit traditional masonry construction where floors are usually designed to fit in with brick coursing. Where it can be done though the reduction in material use leads to lower levels of emboddied energy in the whole construction. I have seen instances particularly where the timber frame systems have been used where an entire course of bricks per floor has been removed with very significant material cost savings to the builder as well. The possible reduction in floor zone is up to 35mm.
Where electrical underfloor heating systems are used it important that the cables are controlled by means of floor stats instead or as well as room stats as there can be a risk of the floor overheating.
Turning the general floor temperature down not only leads to energy savings but also reduces the risks associated with thermal expansion and contraction of the screed and the inpact this has on the finished floor coverings.
The temperature of the underfloor heating system should not exceed 55oC for anhydrite during the comissioning phase and it is generally recomended that this is limited to 45oC during the operation of the floor. This would normally lead to a surface temeprature which is comfortable.
The surface of the screed in operation should feel at best slightly warm to the touch based ont he temerature differential of this (maximum 27oC) and the temperature of the average human hand. If the floor feels hot it is generally too hot.