Well, this wasn't going to be my day 3 subject but today has been a long day and time is short.

At power stations electricity is generated at one voltage then stepped up for distribution. The generator output is usually around 21kV. National Grid distribute at either 275kV or 400kV. DNOs go up to a maximum of 132kV. So, the generated voltage has to be stepped up to the distribution voltage. This is done via a (bloody big) transformer. So, how does then generator connect to the transformer? Big busbars! As I hadn't planned this post I'm a bit short on good pictures but this is a busbar :-
bus1.jpg To give an idea of size those supports are around a foot long.
How do these connect to the transformer? Flexible braids :-
20240817_105443.jpg
All those connections have to be cleaned, Contact grease (known as baby ----) applied, torqued and then ductored. Each joint must have a resistance of 10 micro ohms or less.
Well, that's just the basics. Time is getting on so I'll end it here for now. I'll take some better photos and carry on with this thread soon.