hey guys
we have done an EICR on a 2 bedroom bungalow, the supply is a 25mm 4 core 3 phase SWA to the property, it is supplied from 80amp fuse.
although it is speculative as the cable is underground we reckon the distance is around 600m :fearscream:.
it has being installed around 10 years and no evidence of thermal damage or any concerns of equipment not functioning correctly as per tenants.
the Zdb is 1.89 so disconnection time is not achieved either. the volt drop is around 72volts based on potential load of 80amps.
there are no 3 phase circuits in the installation but it is fully electric so it does have 6 panel heater and an electric hob/oven.
what code would you give based on the voltage drop allowance not being achieved.

exceeding voltage drop for the original thread on Electricians Forums
 

Reply to exceeding voltage drop Electrical Advice in the Electrical Advice area at TilersForums.com

Subscribe to Tilers Forums

Advertisement

Thread starter

Lou

Staff member
Admin
Joined
Location
Staffordshire
Website
https://www.TilersForums.com
What member type are you?
  1. Support Rep (here to provide support only)
Business Name
TilersForums.com

Thread Information

Title
exceeding voltage drop Electrical Advice
Prefix
N/A
Forum
Electrical Advice
Start date
Last reply date
Replies
0

Thread Tags

Tags
None

Which tile adhesive brand did you use most this year?

  • Palace

    Votes: 9 6.0%
  • Kerakoll

    Votes: 14 9.3%
  • Ardex

    Votes: 11 7.3%
  • Mapei

    Votes: 44 29.1%
  • Ultra Tile

    Votes: 18 11.9%
  • BAL

    Votes: 36 23.8%
  • Wedi

    Votes: 3 2.0%
  • Benfer

    Votes: 2 1.3%
  • Tilemaster

    Votes: 21 13.9%
  • Weber

    Votes: 18 11.9%
  • Other (any other brand not listed)

    Votes: 16 10.6%
  • Nicobond

    Votes: 7 4.6%
  • Norcros

    Votes: 3 2.0%
  • Kelmore

    Votes: 4 2.6%
Top