Marginally high CPC end to end readings Discussion ThreadMarginally high CPC end to end readings Electrical Advice

Sure this has come up before but yesterday testing after adding a spur and end to end readings on CPC come out about 0.2ohm over expected reading (was expecting about 1ohm from LL & NN (0.65)

Checked all sockets I could see (some were very old so suspect the sockets themselves might be a contributing factor) other possibility is JB under floor.

Question is would you just report this on meiw, start ripping up floorboards, recommend FI or what?

Earthing system was TT. Zs - 9.75ohms
Also there was quite a bit of original stranded copper in the circuit.

Thanks

Marginally high CPC end to end readings for the original thread on Electricians Forums
 

Reply to Marginally high CPC end to end readings Electrical Advice in the Electrical Advice area at TilersForums.com

Subscribe to Tilers Forums

Advertisement

Thread starter

Lou

Staff member
Admin
Joined
Location
Staffordshire
Website
https://www.TilersForums.com
What member type are you?
  1. Support Rep (here to provide support only)
Business Name
TilersForums.com

Thread Information

Title
Marginally high CPC end to end readings Electrical Advice
Prefix
N/A
Forum
Electrical Advice
Start date
Last reply date
Replies
0

Thread Tags

Tags
None

Which tile adhesive brand did you use most this year?

  • Palace

    Votes: 9 5.6%
  • Kerakoll

    Votes: 17 10.5%
  • Ardex

    Votes: 11 6.8%
  • Mapei

    Votes: 45 27.8%
  • Ultra Tile

    Votes: 21 13.0%
  • BAL

    Votes: 38 23.5%
  • Wedi

    Votes: 4 2.5%
  • Benfer

    Votes: 3 1.9%
  • Tilemaster

    Votes: 22 13.6%
  • Weber

    Votes: 19 11.7%
  • Other (any other brand not listed)

    Votes: 17 10.5%
  • Nicobond

    Votes: 8 4.9%
  • Norcros

    Votes: 2 1.2%
  • Kelmore

    Votes: 5 3.1%
Top