very interesting what are the BS
STANDARDS ON EXPANSION JOINT BAY SIZE?,in screeding ( just to enlighten some peeps ) you would have thought that they would match tile bay size?
i love talking screeds/render and potential faults
Bs8204:1 which covers sand cement screeds does not actually give any specific guidance on bay sizes which is always a bit of a bone of contention amongst screeders and tilers alike.
The generally accepted rules are though that Traditional unmodified sand cement screeds should be split into bays of no larger than 6m in length with an aspect ratio of no more than 2:1 so the max bay would be 6mx6,. This fits in with the acceptable limits for concrete as well. Some will say the max bay length should be no more than 40times the depth.
When it comes to heated screeds I usuall offer the advice given in the NHBC handbook chapter 8 which says sand cement bays should be o more than 15m2 or room size whichever is the smaller.
The standards do go on today that sand cement screeds tend to crack uncontolledly.......
Calcium sulphate screeds are covered in a different part of the standard BS 8207:7:2003 which says that these can be laid to bays much bigger 1000m2 unheated and 300m2 but it does not give advice on aspect ratios so we say unheated 8:1 and heated 6:1.
In both screed toes there are guidelines on additional jointing e.g. Door thresholds and independent heating zones as well as areas of high thermal gain......
The tiling standards then conflict by saying 40m2 in all cases which is about ok for cement but is not even close to correct with gypsum. Trouble is all the standards are written by differentcomittees comprising different "experts". Trouble is the comittee members often have vested interests at some level so it is really difficult to remain objective when looking at the requirements of the standards. The other issue I find is that some of the standard tolerances allow interpretation and you can drive a bus through some of the tolerances.
My view is that BS are for guidance only and should be over ridden by manufacturers requirements. Bit of a nightmare really........