The backer boards are 100% moisture proof. That floor is ready to be tiled.

Uncoupling membrane speaking: if there are 2 sheets of Ditra on the floor, you may apply a polyethylene tape on the joint. If you are worried about any moisture getting to the walls, then you can apply tape to the walls as well.


 
Last edited:
The backer boards are 100% moisture proof. That floor is ready to be tiled.

Uncoupling membrane speaking: if there are 2 sheets of Ditra on the floor, you may apply a polyethylene tape on the joint. If you are worried about any moisture getting to the walls, then you can apply tape to the walls as well.


Thankyou.

That's what I don't get, marmox boards are water proof yet the floor hygrometer on top of them reads 80% RH today at 20 degrees....and the Relative humidity in the floor will be even higher in winter when the floor is colder.

Tempted to spend a day, cover the shower glass and walls with protective coverings and sds up the boards and tile adhesive and start again, lay a 1200g polythene dpm on the bare slab, self level and put down new marmox boards or ditra, but as I can't get under the shower done 100% with the dpm sheet thats likely pointless/fruitless I guess
 
Hiya, concrete floor under the backer boards. Must be a few voids of tile adhesive under the boards. Couple of places you walk you feel the backer boards compress down a little over a small area. I've just drilled, rawl and screwed one defelction area using the large metal board washers to pull the areas down and that seems to work. Maybe I can do that in the remaining coupe of deflection areas, so that I end up with no defelection but obviously dips in the board from what would be level.
 
Self level over that (using moisture tolerant slc) to level it out, then ditra then tile I guess.
I wanted electric ufh for the tiles so was thinking electric ufh cables on top the ditra, but guess that could be a bad thing and make humidity worse as whilst warm air holds more water than cold air and so rh would decrease, but obviously warm air also expands and so may make things worse pushing the moisture upwards - but I could very well be wrong. I could only find a post or two on the internet whether ufh makes moisture better or worse, nothing conclusive.
 
Was that because you had a freshly laid screed or slab though which just needed to dry out ?
I think in this case if I did that it would only be a temporary fix - this slab was laid in the 1970s so it would have dried out a long time ago. As the moisture vapour in the floor is the same in every room (high) It seems to be an ongoing thing. Outside, perimeter drains may help I suppose but I think it's due lack of or failed dpc from the 1970 (dpc weren't regs until mid 1970's so it may or may not have one.
So dehumidifier would work initially but moisture would just build up again afterwards as it comes up through slab from the ground. Thanks for the suggestion though.

I put a piece of vapour barrier on top of the backer boards the other day sealed to the floor and puy the floor moisture meter on top of that - it read 80 percent without the polythene it and 70 percent with it. So that seems it would help, or the liquid dpm but I know you said that's bad practice on top of the backer boards.
I'm going round in circles haha.
 
The similar jobs I have done were flooded at some point and needed a dehumidifier, walls and floors. To attach the Hardie-Becker to the concrete Pros would use SBR, tile adhesive Rawl plugs and screws. The best bond is done on dry surface.

You know how to get on with the project now. Send us pictures during/after
 

Dan

Admin
Staff member
5,100
1,323
Staffordshire, UK
Had this response on electricians forums. Thought I'd post it but I bet this is long sorted.

Rather than covering the issue, find where the moisture is coming from and address from that end, is the outside ground level above the inside, is this earth or a hard standing, path or road, do your gutters overflow, is there a drain of some kind adjacent to the external wall or even under the slab, these and many others can cause moisture inside a building, if you are sure none of these issues exist then the moisture in the slab can be prevented from rising with an epoxy resin tile adhesive, but this may just move the problem into the walls if not laid correctly, better to find out why and address that.

Just looked on the Tilers forum at the pictures and would suggest that the shower or WHB drains may be the problem, check the shower tray for cracks, find the external connection for both and block the drain, fill the shower tray and WHB with water and see if the level drops.
 

Reply to Moisture in floor advice...please in the British & UK Tiling Forum area at TilersForums.com

Subscribe to Tilers Forums

There are similar tiling threads here

Hi there, we have just installed a Hetta UFH system.. they recommend a 6mm plywood over the top...
Replies
3
Views
354
  • Question
What would you Pro’s do? A new extension has electric UFH in the screed which has been brought...
Replies
0
Views
335
Hi, I'm looking for some advice on the best method to level my ensuite floor. The floor is...
Replies
4
Views
467
Hi people I'm in desperate need of advice So my builder who I let go due to poor work has...
Replies
3
Views
1K
I had a small leak in the main water line before the stop tap in my 1950s house. The copper pipe...
Replies
1
Views
2K

Trending UK Tiling Threads

UK Tiling Forum Popular

Advertisement

Thread starter

Joined
Location
Cornwall
What member type are you?
  1. Homeowner
Business Name
None

Thread Information

Title
Moisture in floor advice...please
Prefix
UK 
Forum
British & UK Tiling Forum
Start date
Last reply date
Replies
25

Which tile adhesive brand did you use most this year?

  • Palace

    Votes: 9 5.5%
  • Kerakoll

    Votes: 17 10.4%
  • Ardex

    Votes: 12 7.3%
  • Mapei

    Votes: 46 28.0%
  • Ultra Tile

    Votes: 21 12.8%
  • BAL

    Votes: 39 23.8%
  • Wedi

    Votes: 4 2.4%
  • Benfer

    Votes: 3 1.8%
  • Tilemaster

    Votes: 22 13.4%
  • Weber

    Votes: 19 11.6%
  • Other (any other brand not listed)

    Votes: 17 10.4%
  • Nicobond

    Votes: 8 4.9%
  • Norcros

    Votes: 2 1.2%
  • Kelmore

    Votes: 5 3.0%

You're browsing the UK Tiling Forum category on TilersForums.com, the tile advice website no matter which country you reside. Our UK based online tiling forum has 48,000 members and started out in 2006.

Top