Shower pump wired off shower Discussion ThreadShower pump wired off shower Electrical Advice
Work for a company who sub contracts to the local council and looking for some advice.
In the domestic properties the council have wired a shower pump off the load side of the showers in 2.5mm (40A RCBO) which then serves a 13A switched fused spur to feed the shower pump. I am unsure this is ok as a shower is a fixed load and worried about overload on the 2.5mm?
the council say it’s covered under section 434.2 but this relates to fault current. Can anyone provide some help on the matter,
Thanks
Shower pump wired off shower for the original thread on Electricians Forums
Work for a company who sub contracts to the local council and looking for some advice.
In the domestic properties the council have wired a shower pump off the load side of the showers in 2.5mm (40A RCBO) which then serves a 13A switched fused spur to feed the shower pump. I am unsure this is ok as a shower is a fixed load and worried about overload on the 2.5mm?
the council say it’s covered under section 434.2 but this relates to fault current. Can anyone provide some help on the matter,
Thanks
Shower pump wired off shower for the original thread on Electricians Forums