Voltage Drop Calculation vs OSG Discussion ThreadVoltage Drop Calculation vs OSG Electrical Advice

Hi All,

Hoping to get opinions on Vd calculations for a 1.5mm2 downstairs lighting circuit with an estimated length of 128m!
Length is due to loops at switches (neutrals required) and switched lives feeding various strings of lights.

[ElectriciansForums.net] Voltage Drop Calculation vs OSG


[ElectriciansForums.net] Voltage Drop Calculation vs OSG

Parameters:
Mv/A/m - 29
ib - 2.38
L - 128

Method 1:
Using the standard forumla Mv/A/m x ib x L / 1000 we get 8.82v (3.84%).
This seems unrealistic as it assumes the full load is at the end of the entire circuit length.

Method 2:
An adaptation of the standard forumla is to halve the length provided the load is evenly distributed. Example.
Using Mv/A/m x ib x (L/2) / 1000 we get 4.41v (1.92%).
Given this is a domestic circuit and not a car park, I'm not convinced the load can be assumed to have an even distribution.

Method 3:
Calculate Vd between each point and derive the sum. Example.
Loads have been totalled with loops and corresponding switched lives treated as one length between each point.
The current is adjusted to account for the voltage drop at each point. The result is a small increase from 2.35A to 2.38A.
From the table below, Vd comes out at 4.35V (1.89%).

[ElectriciansForums.net] Voltage Drop Calculation vs OSG


[ElectriciansForums.net] Voltage Drop Calculation vs OSG


OSG Table 7.1(i) suggests a max length of 106m for a 1.5mm2 lighting circuit with a 6A Type B CB on a TN-S supply with 30ma RCD.
The question, Is 128m acceptable provided both EFLI & Voltage drop are within max Zs/3%?

For completeness the max Zs is 5.83Ω and calculated Zs at 2.67Ω. See table below:
[ElectriciansForums.net] Voltage Drop Calculation vs OSG


The circuit could be split but with only 2x 6A MCBs for upstairs/downstairs lights, no spare ways and a new CU out of question, this would inevitably result in two radials off a single MCB. Another option could be to run the loops with 2.5mm2 and the switched lives with 1.5mm2. This could limit choice of accessories as terminal sizes typically accept upto 1.5mm2.

Comments and suggestions appreciated!

Voltage Drop Calculation vs OSG for the original thread on Electricians Forums
 

Reply to Voltage Drop Calculation vs OSG Electrical Advice in the Electrical Advice area at TilersForums.com

Subscribe to Tilers Forums

Advertisement

Thread starter

Lou

Staff member
Admin
Joined
Location
Staffordshire
Website
https://www.TilersForums.com
What member type are you?
  1. Support Rep (here to provide support only)
Business Name
TilersForums.com

Thread Information

Title
Voltage Drop Calculation vs OSG Electrical Advice
Prefix
N/A
Forum
Electrical Advice
Start date
Last reply date
Replies
0

Thread Tags

Tags
None

Which tile adhesive brand did you use most this year?

  • Palace

    Votes: 9 5.6%
  • Kerakoll

    Votes: 17 10.6%
  • Ardex

    Votes: 11 6.8%
  • Mapei

    Votes: 44 27.3%
  • Ultra Tile

    Votes: 21 13.0%
  • BAL

    Votes: 38 23.6%
  • Wedi

    Votes: 4 2.5%
  • Benfer

    Votes: 3 1.9%
  • Tilemaster

    Votes: 22 13.7%
  • Weber

    Votes: 19 11.8%
  • Other (any other brand not listed)

    Votes: 17 10.6%
  • Nicobond

    Votes: 8 5.0%
  • Norcros

    Votes: 2 1.2%
  • Kelmore

    Votes: 5 3.1%
Top