1

1animal1

Hi

I am in the process of fitting a new En suite out and have recently bought a 2m2 heat mat with digital timer. So far I have chased through the walls, ran the electric feed to a fused spur (3A - it's only 150w rating) and ran conduit to the floor ready for the mats cables. The question I have is around the process and a couple of niggles.

The plan is to use the supplied thermal primer compound to prep the newly laid wooden T&G floor boards
(I have enough for 10m2 so thought i'd use that instead of buying something similar), then use a flexible tile adhesive to lay 10mm insulation boards, filling any gaps with adhesive. I'll then prime the insulation boards with the thermal primer before laying the mat, testing the mat, then screeding over ready for tiling with 10mm 60x60 polished porcelain.

I have asked this on another part of the forum and had 1 answer, but the instructions are a bit vague. The cold/hot feed bulky connection that needs setting in tile adhesive? My plan was to hide this in the lower wall, sunk in tile adhesive then a wall tile on top (I've made a recess of about 30mm) - presume the recommendation to sink in tile adhesive is to spread the heat about. Another forum member suggests cutting into the insulation board and screeding over but the instructions say specifically not to do this due to overheating and premature failure, the insulation board obviously retaining any heat the connection gives off. What do you chaps do?

Second query is around the door trim. I am going to buy a chrome z door trim that can be hammered down (with a lump of wood), to accept 25-30mm given the 10mm board, screed, mat and 10mm tiles. Luckily i have a decent depth carpet on the other side to hide this - are there any other trims worth looking at? I'm conscious that it may look tacky in chrome? or is this standard....I am also wondering what to do when screeding, do i put a piece of wood in place of the door trim to screed up to then remove to fit the door trim once tiled?

Thanks in advance and sorry for all the amateur questions :)

Tim
 
F

Flintstone

I think it was me who mentioned about the bulky connector. I have used that method for many many installations without a problem, you just need to dig out about 3mm of the insulation board to make the cold tail connector sit at the same height as the rest of the wires, then it ensures that it all gets coated in levelling compound. Putting the connector in the wall risks having an area that's not properly covered somewhere between the floor and the wall. That's my opinion anyway !
 
Last edited by a moderator:
O

Old Mod

Who's UFH system is this?
I have always sank a small amount of the large cable in to the substrate partly.
You have to, otherwise you're looking at a massively thick layer of slc.
If it's a timber floor, I'll chisel it out, if it's insulation boards I'll cut a channel.
And if you didn't then a small part of the heating cable would have to be left exposed, because of the transition between the two, and that's not right.
I can't see a problem with this, I'd be interested to read their instructions.
 
1

1animal1

Hi, sorry for the late reply, the brand is Nass boards. I'll try and take photos of the instructions tomorrow. As mentioned above though they state that the connector should be under the tiles, encased in adhesive or screed... With an important note to not just cut out the insulation and cover with tape as it risks overheat. That must be the element I missed.... As it wouldn't be encapsulated in adhesive or screed.

Regards the door, do I just use a piece of wood to replace the trim for now until the jobs complete?
 
1

1animal1

Local, I think it was you that commented mate, on reflection my question is void :) thank so much for the advice... Same to everyone else who's commented. I've already ran the conduit but have another piece spare that goes to the floor past the void I've carved out. Fingers crossed it all works when powered up! :) Any thoughts on using the thermal primer to prime the floor boards, it should be OK shouldn't it?
 
O

Old Mod

I had an old teacher :D

Haha that'd explain it!
happy-thumb-up-045.gif
 
1

1animal1

Right, I have the boards down, heating mat down and tested and one layer of Mapei screed...trouble is, the screed only partially covers most of the cables after a few have risen about 2mm above. I know i can use adhesive on the porcelain tiles when laying which will obviously remove the risk of cutting the cables - but i am more worried that the job isn't being done properly - the conductive properties of the screed, depth (which is 5-6mm), the fact that i can't apply adhesive to the floor etc.

Question is, with the total thickness in mind,can i get away with applying adhesive to the tiles - or am i an idiot for not chucking another bag of screed down?
 

Reply to Electric mat installation in the Tiling on Underfloor Heating area at TilersForums.com

There are similar tiling threads here

    • Like
I have a customer who lives in a 200 year old property. The lounge floor he wants tiled which is very thick concrete. He wants electric underfloor heating but I'm concerned he'll lose too much...
Replies
1
Views
152
  • Question
Hi, long time lurker, first time poster. Over the years I've used the good advice that I've read on this forum but with my current project I am a bit stumped. I am renovating an ensuite, it's...
Replies
0
Views
91
  • Question
I've got an AKW Tuff form shower tray with a waste that is 10mm above the tray when fully screwed in. The Tiler laid my 5mm hex mosaic tiles on a 2mm bed, so obvs wasn't going to drain. I took...
Replies
6
Views
2K
  • Question
Hi all, I am planning to tile a full height panel of split face tiles to sit 3” behind a log burner on a plaster render on blockwork wall. I’m planning to score and scrape the paint off the...
Replies
5
Views
1K
  • Question
Hi all, I've laid some Arditex NA over the kitchen floor area (not under cabinets. The area is 4.5m x 1.8m. The top third of the room is totally level. The remainder of the room has a slope...
Replies
3
Views
1K
Posting a tiling question to the forum? Post in Tilers' Talk if you are unsure which forum to post in. We'll move it if there's a more suitable forum.

Advertisement

Top