Ahhhhh...... found it. Or at least part of it. In the June update of BS5385 Part 1.... but now they should amend part 4 to suite!
6.1.1.3 Tanking
In Wet areas, e.g. showers, wet rooms and steam rooms, substrates should be protected with a suitable proprietary tanking membrane system.
The weight capacity of the tanking system should be capable of carrying the load of the tiles and adhesive. If mechanical fixings are to be used the membrane manufacturer should be consulted.
Where the substrate is to be protected with a tanking membrane the weight restrictions of the installation might be reduced therefore the membrane manufacturer should be consulted.
NOTE This can be a proprietary sheet membrane or a liquid applied water impermeable product.
6.1.1.3 Tanking
In Wet areas, e.g. showers, wet rooms and steam rooms, substrates should be protected with a suitable proprietary tanking membrane system.
The weight capacity of the tanking system should be capable of carrying the load of the tiles and adhesive. If mechanical fixings are to be used the membrane manufacturer should be consulted.
Where the substrate is to be protected with a tanking membrane the weight restrictions of the installation might be reduced therefore the membrane manufacturer should be consulted.
NOTE This can be a proprietary sheet membrane or a liquid applied water impermeable product.