Collective thoughts about issue… Pub kitchen Electrical Advice

Tilers Forums Official Sponsors

Collective thoughts about issue… Pub kitchen Discussion ThreadCollective thoughts about issue… Pub kitchen Electrical Advice

Been asked to look at local pub kitchen as a circuit was tripping.

The circuit appears to be a repurposed cooker circuit, fed in 6mm t&e to two MK double sockets. Second socket is fed in 2.5 from the first.
The load is 2x twin fryers… at 2.6kW per unit… so 4 units, but only 3 are ever used as the last one is positioned under a shelf.
The RCBO is only a 20A…. But I don’t know if that’s a case of “all that was in the van at the time” or a purposeful decision considering the load. Ie keeping the load limited to protect the sockets themselves.

I think it would be ok to uprate to a 32A…. And change that little bit of 2.5 to 4.0mm
The MK sockets are the older type, so not the newer less quality ones. IMG_6834.jpegIMG_6832.jpegIMG_6828.jpeg

Collective thoughts about issue… Pub kitchen for the original thread on Electricians Forums
 

Advertisement

Weekly Email Digest

Back
Top

Click Here to Register for Free / Remove Ad