Do crimped connections in a choc box in an inaccesssible location comply with regulations?

  • Thread starter Thread starter peterinreading
  • Start date Start date
  • Tags Tags
    box

Tilers Forums Official Sponsors

The relevant regulations are I think as follows:

BS 7671 513.1: cable joints must be accessible except where allowed by 526.3

which is covered by ...

BS 7671 526.3 (iv) joints made by welding, soldering, brazing or compression (which covers crimped connections)

So far so good. But:

526.5 (iii) Every termination and joint shall be in an enclosure partially formed or completed with non-combustible material.

This I think does not cover a choc box which is as far as I can make out is made of polyproplyne which is combustible.

Am I missing something?

I know you will all say I should use Wago connectors in a Wago box which is obviously correct, but I want to know how I should treat existing inaccessible crimped connections in a choc box in an inspection.

Continue reading...
 

Advertisement

Thread Information

Title
Do crimped connections in a choc box in an inaccesssible location comply with regulations?
Prefix
N/A
Forum
Electrical Advice
Start date
Last reply date
Replies
0

Thread Tags

Tags Tags
box

Advertisement

UK Tiling Forum

Thread statistics

Created
peterinreading,
Replies
0
Views
11

Thread statistics

Created
peterinreading,
Replies
0
Views
11

Weekly Email Digest

Back