Poor preparation for shower wall tiling?

Tilers Forums Official Sponsors

Who is at fault here? Our builders built a stud wall and secured backer board to it. Our tiler then proceeded to tile onto it. We had multiple tiles crack along one vertical line where the two backer boards met. Upon removing tiles, one backer board was only secured with 6 screws and there were no horizontal batons in the stud. The vertical batons are 600mm apart.
1606397927897.png

Builder is claiming the stud wall is good enough but agrees there should have been more screws. He is claiming that tiler should have checked so won't take responsibility for re-do of tiling.
Tiler is claiming it was not his responsibility to check whether the wall was sufficiently prepared for him to tile onto and that there should definitely be horizontal batons.
Any advice much appreciated - we are stuck in the middle!
 
Builder is responsible for the framing and boarding ,it’s his bag. 600mm spacing is to much in that situation, should be more like 400mm spacing. Also the stud on the left is not connected at the top.
 
I'd say the builder is mainly to blame but I think the tiler should also take some responsibility. If I had to tile that wall I'd either have a word with the builder first or put in some extra screws and fibreglass tape the joints.
 

Advertisement

Thread Information

Title
Poor preparation for shower wall tiling?
Prefix
N/A
Forum
Tanking and Wetrooms
Start date
Last reply date
Replies
5

Advertisement

UK Tiling Forum

Thread statistics

Created
emilytwaite,
Last reply from
Rae,
Replies
5
Views
1,973

Thread statistics

Created
emilytwaite,
Last reply from
Rae,
Replies
5
Views
1,973

Weekly Email Digest

Back