My last statement was slightly untrue 😀
Ref to the RCD with earth, (the old RCD) they have not been used in domestic installations for a long time and are usually 50ma 80ma and 100ma that ar not permitted.
Standard 32ma RCD do not need and earth they have a coil on the live a coil on the neutral then there is a coil between the two, if the polarity on the first two coils differs then the 3rd coil will actuate a trip.
The property and and circuits however do need an earth or be bonded there are exceptions that can be found in BS7671:2008 (the good book)
Also an RCBO is just simply an RCD (standard) with built in MCB (over current protection)
So in answer to your question the AHT system is compatible with All Regulation RCDs with or without an earth grid.
The fact still remains the AHT system is "Double insulated" which means it is harder to damage and expose the live conductor hence the reason it is give CLASS II status.
Also take into account the fabric of the property be earthed and various means of supplimetry bonding.
Please also not that the design purpose of the AHT system is it does not need an earth grid, the fact is Bs7671:2008 and previous requires that in bathrooms a supplimentry earth is installed above and I am happy it is (Helps the Adhesive Key in Nicely).
Just spoke to a gentleman called Dave, in the technical department at Crabtree (major manufacturer of circuit protection equipment) and he has advise that all their single module RCBO's are supplied with an earth fly lead. These earth leads are typically coloured white or cream, which designates them as functional earths, which means that an earth is required to ensure that the RCD part of the RCBO operates correctly in the event of a fault.
The purpose of the earth fly lead on single module RCBO's is to ensure that the breaker trips in the event of the neutral of the circuit being lost.
The conclusion is that you do require an earth (CPC) for circuits that are connected to RCBO's or RCD's that have an earth fly lead.
Why else would the manufacturer's have the earth fly lead, decoration?
There may also be other RCD's or RCBO's that require the earth to be connected but as yet I have not received any information back from the manufacturer's that I have requested information from.
Therefore, I have to conclude that Class II equipment such as AHT underfloor heating mats are NOT compatible with all RCBO's & RCD's, unless a seperate earth grid is installed over the top of the system.
So, for the Tilers in this forum, you may or may not have to install an earth gird over the heating, it depends on the method of earth leakage protection (RCD / RCBO), if you choose to install an Class II system such as AHT.