If I'am allowed to quote - from a major adhesive manufacturers 'bible'.
The heating pipes should be installed according to manufacturers instructions, fixed down and tested prior to being encapsulated in a screed or levelling compound.
If the pipes have been laid in a reinforced sand/cement screed, this must be allowed to dry fully prior to tiling.
A sand/cement screed should be left for 3 weeks with the underfloor heating off, to dry.
After this period the heating system should be turned on and the temperature raised by a maximum of 5degrees/day until the maximum recommended operating temperature is achieved.
This temperature should be maintained for 3 days and then the system turned off and the screed allowed to cool to 15degrees before tiling commences.
If a suitable polymer-modified levelling compound is used to cover the pipes instead of a sand/cement screed, the drying time will be considerably shorter.
Ensure that the cured surface of the floor is rigid, sound, clean, dry and free from any contaminating barrier. Porous or dense substrates must be primed and also impervious surfaces with the relevant manufacturers primers.
Fix the tiles.
Allow to cure. Keep the warming system turned off for at least 5 days to allow the cement to cure. Bring the system up to its operating temperature gradually in stages of 5degrees/day.
I hope this is of help.
You need to obtain the exact type of screed laid and the preparation prior to tiling it received