If I'am allowed to quote - from a major adhesive manufacturers 'bible'.
The heating pipes should be installed according to manufacturers instructions, fixed down and tested prior to being encapsulated in a screed or levelling compound.
If the pipes have been laid in a reinforced sand/cement screed, this must be allowed to dry fully prior to tiling.
A sand/cement screed should be left for 3 weeks with the underfloor heating off, to dry.
After this period the heating system should be turned on and the temperature raised by a maximum of 5degrees/day until the maximum recommended operating temperature is achieved.
This temperature should be maintained for 3 days and then the system turned off and the screed allowed to cool to 15degrees before tiling commences.
If a suitable polymer-modified levelling compound is used to cover the pipes instead of a sand/cement screed, the drying time will be considerably shorter.
Ensure that the cured surface of the floor is rigid, sound, clean, dry and free from any contaminating barrier. Porous or dense substrates must be primed and also impervious surfaces with the relevant manufacturers primers.
Fix the tiles.
Allow to cure. Keep the warming system turned off for at least 5 days to allow the cement to cure. Bring the system up to its operating temperature gradually in stages of 5degrees/day.
I hope this is of help.
You need to obtain the exact type of screed laid and the preparation prior to tiling it received
![]()
The screed was lafarge gyvlon : Lafarge Gyvlon Anhydrite based Calcium Sulphate Flowing Screed i'll find out more when we meet in a few days (last one was postponed as one crucial person was held up ) what i'm still needing clarification on is when they are talking about increasing the temperature in 5C increments is that the control (miramix) near to the mainifold that has min- 40-45-50 etc on it or the thermostatic controls dials on on each zone? Like ive mentioned already a couple of times the miramix was set on 'minimum' for 4 days (post tiling but not grouted) but the thermostat dials were put immediately and left on 27C. Was this wrong or does only the miramix setting matter in this case? Is there another section of the forum more suitable for me to post this UFH question as id really like the answer before we meet after the weekend?
Thanks again. Gubbins