UPS - Earth - RCD what is required, and testing?

Tilers Forums Official Sponsors

CAUTION! The UPS must be connected to a grounded AC power outlet with fuse or circuit breaker
protection. DO NOT plug the UPS into an outlet that is not grounded. If you need to de-energize this
equipment, turn off and unplug the UPS.

I read this as meaning an earth rod is required, as the whole idea of a UPS it to give power when the grid is down, and if the grid is down one can't rely on any earth from the DNO be it TN-S or TN-C-S.

As to linking neutral to earth during a power failure, nothing in the spec says it does this, the output is 6 x 13 amp sockets, 3 UPS and 3 direct, and no reference to RCD or any earth fault detection being built into the unit. Manual is available here I wonder if this is normal or not?

I have a far larger unit, 5 kW on 6.4 kWh battery, which does link earth and neutral with a power failure, it has got an earth rod, earth fault detection in the inverter plus RCD type A sockets, and my RCD tester shows they trip at 21 mA and well within 40 mS and a reasonable loop impedance. So I'm alright, Jack, but 780 watt is a far smaller unit, with equipment being plugged directly into the UPS with 13 amp socket. At half load only got 9 minutes, so not a big deal, mine 6 hours and still 37% left running whole house with a power failure only selected sockets, so may never run out if enough sun during the day.

So with the small UPS is lack of earth rod and RCD a real problem, or something we can turn a blind eye to?

Continue reading...
 

Advertisement

Thread Information

Title
UPS - Earth - RCD what is required, and testing?
Prefix
N/A
Forum
Electrical Advice
Start date
Last reply date
Replies
0

Thread Tags

Tags Tags
None

Advertisement

UK Tiling Forum

Thread statistics

Created
EricMark,
Replies
0
Views
24

Thread statistics

Created
EricMark,
Replies
0
Views
24

Weekly Email Digest

Back