Quick drop in at a house on way home…. Customer couldn’t reset mcb for rfc.
Power off at board, outgoing cables disconnected… I was getting 200V between the neutral bar and the earth bar within the CU.
With the CU mainswitch on, I am getting a voltage on the disconnected live cables.
Have not disconnected the neutrals yet,
For now, I have left the cables disconnected, and the rest of...