You'd need to continuity test the heating wire and the outer earth wire if there is one then you'd need to insulation test the wire using a 1000v mega tester. You might need to get a bit creative to mega test the insulation if the heater doesn't have an earth wire running inside it, the damaged area would need to be exposed.

Problem with heat shrink tubing is you'd need to cut the wire completely to get it on then rejoin afterwards.

If you damage UFH wires my best advice would be to get a sparky in who specialises or has lots of experience with UFH systems. This especially goes with UFH in a bathroom which is far more likely to give people a fatal shock if it's faulty.

If the rcd detected any irregularities it would trip the power. If there is anything problems with the ufh, this is far more likely to happen than someone meeting a shocking death (no pun intended) ufh controllers also monitor this and again will trip the power if there is a problem. It is highly unlikely for anyone to get an electric shock from ufh.

Even older fuse box's are likely to trip with irregular currents from ufh running through them.
 
M

Marvo

RCD's save lives but there's no guarantee, some people die from shocks of less that 30mA, it's just a numbers game where most will survive but some won't.

Older fuse boxes often don't have RCD protection, only overload protection. The fuses in them only protect the circuits from overload damage, they don't protect people from getting fatal shocks.

All the UFH controllers I've experienced are just a temperature control, they don't include shock protection or earth leakage protection. Technology progresses and systems are constantly made safer so I'd be interested to read up on the controllers you refer to if you can give me a link.

People getting shocks in a bathroom are far more likely to be killed than in other locations. The electrical regs recognize this and address it by declaring bathrooms 'special locations' that require extra protection measures.

It probably is statistically unlikely to get a shock from an undamaged UFH system as you say but if the wire is damaged under the floor and there's moisture around the damaged area it's highly likely it would cause someone in bare feet to get a shock. There's many variables involved so it might just be an occasional tingling or 'static' sensation when touching taps or a towel rail or it might be worse.

My advice still stands, if the UFH heater tape or wire is damaged I'd strongly advise an official repair by someone with experience who can test the system afterwards.
 

Reply to Ufh Cable Might Be Damaged. in the Australia Tiling Forum area at TilersForums.com

Subscribe to Tilers Forums

There are similar tiling threads here

Hi everyone, I'm looking for some advice on final floor buildup. We're installing a shower tray...
Replies
0
Views
2K
Hi everyone, I'm looking for some advice on final floor buildup. We're installing a shower tray...
Replies
0
Views
1K
Hi everyone, I'm getting towards the end of a major renovation that has taken 4+ years so don't...
Replies
9
Views
4K
Hi I joined and posted on this forum little while ago regarding our bathroom and ensuite wetroom...
Replies
12
Views
8K
L
ok so im on a job with 3 bathrooms to go at. Ive got 2 of them prepped with deltaboard...
2
Replies
19
Views
6K

Advertisement

Thread starter

Sean Kelly

Arms
TF
Joined
Location
Ruislip

Thread Information

Title
Ufh Cable Might Be Damaged.
Prefix
N/A
Forum
Australia Tiling Forum
Start date
Last reply date
Replies
16

Thread Tags

Tags
ufh

Which tile adhesive brand did you use most this year?

  • Palace

    Votes: 9 5.5%
  • Kerakoll

    Votes: 17 10.4%
  • Ardex

    Votes: 12 7.3%
  • Mapei

    Votes: 46 28.0%
  • Ultra Tile

    Votes: 21 12.8%
  • BAL

    Votes: 39 23.8%
  • Wedi

    Votes: 4 2.4%
  • Benfer

    Votes: 3 1.8%
  • Tilemaster

    Votes: 22 13.4%
  • Weber

    Votes: 19 11.6%
  • Other (any other brand not listed)

    Votes: 17 10.4%
  • Nicobond

    Votes: 8 4.9%
  • Norcros

    Votes: 2 1.2%
  • Kelmore

    Votes: 5 3.0%
Top