Discuss UFH Running cost difference with 6mm verses 10mm insulation board in the Canada Tile Advice area at TilersForums.com.

AliGage

TF
Esteemed
Arms
Subscribed
4,531
1,188
Peterborough, England
I would insulate either wooden or concrete substrates.

1) I wouldn't want to warm the chipboard or ply floor. We all know timber dont react well to temoreture chantes.

2) The purpose of UFH is to warm the top, finished covering. Make sense to spend the little extra over concrete to ensure it works as efficiently as possible. If its losing heat into a big slab of concrete itll never reach desired tempreture.
 
495
1,118
Somerset
Sort of. No what I meant was the difference in efficiency between 10mm and 6mm when it comes to running cost is likely to to have little impact.

Now the science bit.... Haven't got the figures available for chipboard but if you do a rough u-value calculation for a floor of 10m2 (5mx2m) with one exposed wall of 5m and a screed of 10mm having a thermal resistance of 0.0045m2K/W

you get a u-value of 0.61w/m2K with the 6mm board (assuming the insulation has an r-value of 0.023W/mK and a value of 0.58w/m2k with the 10mm board. In other words not much difference. Probably pennies per year difference rather than hundreds of pounds.

Interesting comments - yet the technical data from an underfloor heating company gives the following data on U-values (W/m K) for its supplied boards:

6mm - 4.50
10mm - 2.70
20mm - 1.35
50mm - 0.54

So the difference in value means the 10mm board is 40% more efficient than the 6mm board. (source - Warmup Brochure - Warmup Product Brochure | Warmup)

Under floor heating cable radiates heat equally out from its outer edge, and most of the heating cable manufacturers have calculated the impact of the boards in reducing the amount of heat radiated downwards into the sub-floor. Now without having done the tests myself I have to accept that their claims are at least worth consideration even though I cannot validate them. Manufacturers are now often recommending the addition of some reflector material (either a foil or reflective priming solution) to reduce the downwards radiation as well as insulation board.

I know from my training on installation of ufh that we were told that insulation boards are not mandatory but their use has been calculated as measurably reducing the amount of energy consumed in achieving and maintaining a standard room and floor temperature. 10mm boards were recommended as the best compromise between measurably reducing running costs and not excessively increasing floor height.

Perhaps someone from U-Heat could add to this thread. I am with other tilers posting in this thread- are we being duped into installing expensive insulation tiling boards to no great benefits? Who does the research and has it been corroborated by independent tests?
 
Last edited by a moderator:
Q

Qwerty

On UFH installs I have done with 6 & 10 mm boards the 10 mm have always warmed up quicker.
Out of curiosity I'm going to perform my own test this weekend. I will place a piece of 6mm, 10mm & 20mm Marmox board outside on my patio. I will leave them there overnight then in the morning record the surface temperature of each (will be the same). I will then boil two identical pans of water and place them on the boards leaving them there for a few minutes. I will then remove the pans, recording the temperature again in 30 second intervals (up to 5 minutes). At the end I will lift the boards. & record the patio temperature! Surely this will show that the thicker board retains (reflects) more heat for longer!?!?
 
G

Gazzer

On UFH installs I have done with 6 & 10 mm boards the 10 mm have always warmed up quicker.
Out of curiosity I'm going to perform my own test this weekend. I will place a piece of 6mm, 10mm & 20mm Marmox board outside on my patio. I will leave them there overnight then in the morning record the surface temperature of each (will be the same). I will then boil two identical pans of water and place them on the boards leaving them there for a few minutes. I will then remove the pans, recording the temperature again in 30 second intervals (up to 5 minutes). At the end I will lift the boards. & record the patio temperature! Surely this will show that the thicker board retains (reflects) more heat for longer!?!?

Interesting ! :thumbsup:
 
J

JimboD

On UFH installs I have done with 6 & 10 mm boards the 10 mm have always warmed up quicker.
Out of curiosity I'm going to perform my own test this weekend. I will place a piece of 6mm, 10mm & 20mm Marmox board outside on my patio. I will leave them there overnight then in the morning record the surface temperature of each (will be the same). I will then boil two identical pans of water and place them on the boards leaving them there for a few minutes. I will then remove the pans, recording the temperature again in 30 second intervals (up to 5 minutes). At the end I will lift the boards. & record the patio temperature! Surely this will show that the thicker board retains (reflects) more heat for longer!?!?

Interesting, but it only tackles one half of the issue. Placing boards over a big cold heat absorbing mass like a concrete floor (or patio) makes sense. It provides a barrier and allows the UHF to heat the tiles instead. The thicker the better I assume in this case. What is less clear is when the UHF is on wooden upstairs flooring where there is central heating in the rooms below and the std 100mm insulation between the floor joints. Here the UHF isn't struggling to heat up a cold mass so what is the extra benefit of adding boards in this situation (beyond creating a better tiling surface).

Perhaps there is another experiment here that factors patio vs perhaps kitchen table as the substrate?
 
Q

Qwerty

I spent a bit of time this morning performing the tests. I performed the test on the garage screed, then 18mm WBP, 10mm Marmox then 6mm Marmox. I chose not to use any 20mm boards as realistically most of us never use them.

y6yvutyt.jpg


To ensure continuity the water (2 pints) was boiled then left one minute (whilst walking into the garage) before temperature was checked to ensure test was fair (stage 1).
The water in the pan was left on each of the surfaces for 5 minutes, with the water temp being checked halfway through (stage 2).
After 5 mins the pan was removed and the substrate surface temp taken (stage 3).
Underside temp of substrate taken (stage 4).
Area of garage floor directly underneath where pan was present in substrate taken (stage 5).
Each substrate left stood up with both sides exposed for 5 minutes and then surface temps taken again (stage 6 for topside and stage 7 underside where pan had been sat).

Outside air temperature was 6*c. Garage floor was an even 5.8*c. All of the ply & boards read 5.8*c too which was a good start.
ry3ubuja.jpg

y9yremy8.jpg

edubahuh.jpg

age5aryt.jpg
 
Q

Qwerty

So here are the test results................






Control Test - Garage floor
Stage 1- Starting water temp - 68.5*c
re7y6e3u.jpg

Stage 2- Halfway water temp - 63.8*c
y5e6apy2.jpg

Stage 3- Substrate surface temp - 17.6*c
y6aby4e2.jpg

Stage 4- Substrate underside temp - N/A
Stage 5- Garage floor temp - N/A
Stage 6- Substrate surface temp (after 5 mins) -12.3*c
3u4adyma.jpg

Stage 7- Substrate underside temp (after 5 mins) - N/A
 
Q

Qwerty

Conclusions

No science lab standard I know, but it clearly shows that the thicker the insulation boards the better!
The bare floor clearly absorbed a lot of heat rather than reflecting it back which is to be expected. The ply being so dense absorbed more heat and this transferred through it to the underside much more than either of the Marmox boards. The ply also lost its heat much faster.
The Marmox boards performed best. The 10mm board reflected back (and retained) a lot more heat than any of the others. The heat on the top of the Marmox boards could be seen by a circle. This even transferred through to the underside of the 6mm board as well as being visible as "sweating" onto the garage floor!

Out of curiosity I checked a few things 10 minutes later and found the 12mm Marmox retained the heat best (@ 8.7*c) and the 6mm was just 6.5*c.
etety4a6.jpg


The floor where the 6mm Marmox had been was still 6.0*c after 10 mins whereas the floor where the 10mm & ply still read 5.8*c!!
qanyvuqu.jpg



I'm continuing to use 10mm boards where I can thanks. It just makes sense! I appreciate that ply retains temperature but my tests also showed it was a massive heat sink and didn't retain it well.

Insulation boards work.....simple as that really.
 
Last edited by a moderator:

Reply to UFH Running cost difference with 6mm verses 10mm insulation board in the Canada Tile Advice area at TilersForums.com

Subscribe to Tilers Forums

There are similar tiling threads here

1950s ex council house, solid concrete floors, about to have the ground floor tiled - hall...
Replies
2
Views
1K
D
Replies
7
Views
23K
Deleted member 57709
D
R
    • Like
well have been told all sorts about ufh so decided to test for my self i wanted to know the...
Replies
7
Views
2K
Old Mod
O
G
hey guys In 2 minds wether to put underfloor heating in my kitchen. I've currently got a...
Replies
9
Views
15K
Old Mod
O
What's everyone's preferred method of securing loose wire element to insulation board before...
Replies
21
Views
3K
slythetiler
S

Advertisement

Thread Information

Title
UFH Running cost difference with 6mm verses 10mm insulation board
Prefix
N/A
Forum
Canada Tile Advice
Start date
Last reply date
Replies
51

Which tile adhesive brand did you use most this year?

  • Palace

    Votes: 5 5.0%
  • Kerakoll

    Votes: 8 8.0%
  • Ardex

    Votes: 6 6.0%
  • Mapei

    Votes: 25 25.0%
  • Ultra Tile

    Votes: 14 14.0%
  • BAL

    Votes: 27 27.0%
  • Wedi

    Votes: 3 3.0%
  • Benfer

    Votes: 2 2.0%
  • Tilemaster

    Votes: 19 19.0%
  • Weber

    Votes: 18 18.0%
  • Other (any other brand not listed)

    Votes: 10 10.0%
  • Nicobond

    Votes: 5 5.0%
  • Norcros

    Votes: 3 3.0%
  • Kelmore

    Votes: 1 1.0%
Top