Hi Sean Kelly
Pretty much spot on although if I was notified in the first instance, I would of gone in with my sparky( have done 2 of these in the past and have been compensated as it was a manufacturing fault ) and if it definitely was below tiles. started with taking up the tile with the cold join beneath it and if it wasn't that joint then move on to the end tail (termination join) At this point if we couldn't get it working, I would have called in the proffessionals and would have paid them to sort it. There are only 2 joints in any one mat, 99% of the time if it fails, it will fail there.
Pretty much spot on although if I was notified in the first instance, I would of gone in with my sparky( have done 2 of these in the past and have been compensated as it was a manufacturing fault ) and if it definitely was below tiles. started with taking up the tile with the cold join beneath it and if it wasn't that joint then move on to the end tail (termination join) At this point if we couldn't get it working, I would have called in the proffessionals and would have paid them to sort it. There are only 2 joints in any one mat, 99% of the time if it fails, it will fail there.