Alan, quick question.
In all the failures you have seen on these screeds, is it always the fixers lack of understanding about the screed (without proper prep) that the instillation has failed?
It's not as easy a question to answer yes or no to. I have come across many instances where the fixer believes he has done everything by the book based on a book written for example by the adhesive manufacturer. I often get told "I used the correct materials, primers and adhesives etc". When in actual fact despite assurances from adhesive manufacturers they are inherently flawed. Most of the failures I have come across are due to 1 or a combination of 2 issues.
1. Excessive moisture in the screed
There are many reasons why this cold happen
2. Inappropriate use of primers leading to the primer-screed bond failing
It could be that the primer needed to be diluted but the manufacturers instructions did not say so. It could be that the screed surface was too dense because it was in sufficiently sanded (this is one of the potential issues with the low Laitance screeds that are available in the market where people say "they don't need sanding") or it could be something else.
the latter reason is one of the reasons I have tried to promote primer less systems where possible because it removes a risk.
When assessing such issues I always try not to apportion blame or responsibility but sim outline what has gone wrong. This is sometimes diffiucult because everyone wants to blame someone and its often no one persons fault...
Ettringite is actually quite a rare thing to see these days in terms of reasons for failure.