Marginally high CPC end to end readings Electrical Advice

Marginally high CPC end to end readings Discussion ThreadMarginally high CPC end to end readings Electrical Advice

Sure this has come up before but yesterday testing after adding a spur and end to end readings on CPC come out about 0.2ohm over expected reading (was expecting about 1ohm from LL & NN (0.65)

Checked all sockets I could see (some were very old so suspect the sockets themselves might be a contributing factor) other possibility is JB under floor.

Question is would you...
 

Subject: Advice Needed on NVQ Level 3 and NAPIT/NEICC Registration Electrical Advice

Subject: Advice Needed on NVQ Level 3 and NAPIT/NEICC Registration Discussion ThreadSubject: Advice Needed on NVQ Level 3 and NAPIT/NEICC Registration Electrical Advice

Hey all,
I’m looking for some advice regarding my qualifications and registration. Here’s where I’m at:
• Level 2 Diploma in Electrical Installations (Buildings and Structures) – 600/5498/0
• Level 3 Diploma in Electrical Installations (Buildings and Structures) (2365-03) – 600/5499/2
• Level 3 Award in the...
 

Extractor fan connection Electrical Advice

Extractor fan connection Discussion ThreadExtractor fan connection Electrical Advice

Hi,

I hope you can help me please. I am replacing extractor fan with timer and PIR (100TM model) to model 441625A (100T) with just the timer. With the old one (the one with orange drawing) 3 wires are connected in the same order Ls,N, L (L at the bottom) and all works fine. It is activated on movement (movement only, pulling a light string without movement in the bathroom does not activate fan)...
 

Pen fault pme fault detection? Electrical Advice

Pen fault pme fault detection? Discussion ThreadPen fault pme fault detection? Electrical Advice

So I’ve been looking for a pen fault detection device for hours and only found like 1 which is sold out ?! Any idea or urls anyone can send for a pen device. I’ve found a lot of pme faults detection for ev. But I want pen. Or does it not matter I thought it did matter

Pen fault pme fault detection? for the original thread on Electricians Forums
 

Fire Damper Actuators Electrical Advice

Fire Damper Actuators Discussion ThreadFire Damper Actuators Electrical Advice

Hello

Working on a site with dampers fitted on the ducting which need fire shut offs connected to the fire panel via an actuator.

The actuators have 4 contacts “Damper Closed NO and NC” and “Damper Open NO and NC”.

Presuming they need a NC contact so the actuator operates and closes the damper when the alarm goes off but not sure which NC contact to utilise.

Any insight appreciated.

Thanks.

Fire...
 

Switch won't physically operate Electrical Advice

Switch won't physically operate Discussion ThreadSwitch won't physically operate Electrical Advice

I have this gewiss switch that is being used as a switch for a hot tub.
www.gewiss.com

VERTICAL FIXED INTERLOCKED SOCKET OUTLET - WITH BOTTOM - WITHOUT FUSE-HOLDER BASE - FOR HEAVY-DUTY USE - 2P+E 63A 200 - 250V - 50/60HZ 6H - IP66 | Gewiss...

 

DC wiring circuit for controlling fans Electrical Advice

DC wiring circuit for controlling fans Discussion ThreadDC wiring circuit for controlling fans Electrical Advice

Hi All,

Trying to put together a circuit to make some fans work via a thermostat. The thermostat will pick once a certain temp reaches which will notify the system the temp has increased and at the same time allow the fans to turn on as the contact in thermostat is normally open and closes once the temp reaches to the set limit.

Had a few doubts not sure if I can use the...
 

Shaver socket in cabinet not accepting toothbrush? Help please Electrical Advice

Shaver socket in cabinet not accepting toothbrush? Help please Discussion ThreadShaver socket in cabinet not accepting toothbrush? Help please Electrical Advice

Good afternoon

I have recently had a bathroom makeover and had the existing shaver socket removed as I purchased a cabinet with socket enclosed. However, my oral b toothbrush 2 pin doesn't fit into thr 230v 2 pin socket in the cabinet whereas i had no issues with the previous socket.. I'm not sure what I need to buy in...
 

TT supply for hot tub Electrical Advice

TT supply for hot tub Discussion ThreadTT supply for hot tub Electrical Advice

Hi,

I have recently had a hot tub fitted and am not comfortable with it being supplied directly from TN-C-S supply. I’m looking for someone to modify to TT, but struggling to find anyone locally who can help.

Location - Warrington, Cheshire.

Thanks.

TT supply for hot tub for the original thread on Electricians Forums
 

Gas cooker change to an electric cooker Electrical Advice

Gas cooker change to an electric cooker Discussion ThreadGas cooker change to an electric cooker Electrical Advice

Hi everyone, we currently have a gas cooker which is getting old and needs to be replaced. The problem is that the width is 55cm and there are few gas cookers of this size nowadays. The question is - how easy would it be to change to an electric cooker? Our current gas cooker has a 13amp connection for cooker lights etc but obviously this wouldn't be sufficient for an...
 

Shared immersion heater circuit Electrical Advice

Shared immersion heater circuit Discussion ThreadShared immersion heater circuit Electrical Advice

Hi everyone

Is it permissable to connect 2 immersion heaters to one RCBO and supply cable?

I'm installing a water cylinder (which has 2 immersions) in a new utility room, which used to be a kitchen.

I want to repurpose the old cooker supply cable which is 10mm. If it's legal, I want to feed both immersions vis seperate DP switches, but they will share the same RCBO in the consumer...
 

Contactor not latching Electrical Advice

Contactor not latching Discussion ThreadContactor not latching Electrical Advice

Hi all.

Is it too early to wish everyone a happy Christmas?😅

Looking for a little bit of help regarding a contactor.

I got a call to look at a 230v heavy duty mixer/blender in a busy hospital kitchen. It has stop/start buttons and a contactor within the appliance itself. Contactor is a Teco, 3 pole normally open. When I arrived I assumed it was the contactor. Start button wasn't energising the coil...
 

Difference between c&g 2391-52 and eal 2625 Electrical Advice

Difference between c&g 2391-52 and eal 2625 Discussion ThreadDifference between c&g 2391-52 and eal 2625 Electrical Advice

Hi,

I am looking to take my initial verification and periodic inspection course and from what I can see online there are two options to go for as mentioned in the title. From what I can see there isn't much difference in these course as to the level and recognition. I was curious what other experience is in the difference between these two bodies that offer the...
 

Bnc cable with power messed up for cctv Electrical Advice

Bnc cable with power messed up for cctv Discussion ThreadBnc cable with power messed up for cctv Electrical Advice

Hi I have stupidly cut the cable to push through the wall . Idea was to join them back together.

There's 2 wires inside blue and a white one. The white one has copper strands exterior around it.

When I joined it back together. The camera didn't work.

I'm unsure if it's down the cable I've knackered now from that bit. Or I might have nicked it from outside when trying...
 

Groups or Organisations that volunteer for needy/vulnerable Electrical Advice

Groups or Organisations that volunteer for needy/vulnerable Discussion ThreadGroups or Organisations that volunteer for needy/vulnerable Electrical Advice

Hello,

Is anybody aware of any UK groups or organisations that volunteer or subsidise trades people to do work for; Low income/Vulnerable/Needy people?

For example homeowners in rundown properties who do not have money to employ an electrician to make safe an outdoor socket or fix a utility room socket which is currently running...
 

EICR for a rental property Electrical Advice

EICR for a rental property Discussion ThreadEICR for a rental property Electrical Advice

hi got an EICR report completed yesterday for a rental property. Still waiting for the report. Told there is one c1 and a number of c2 observations.

Electrician appears to want a lot of money to fix issues. He is also saying if i use someone else to fix issues, i will need to get the EICR redone.

Views?

EICR for a rental property for the original thread on Electricians Forums
 

When to use AFDD’s Electrical Advice

When to use AFDD’s Discussion ThreadWhen to use AFDD’s Electrical Advice

We currently install industrial washing machines, driers and finishing equipment. These can be three phase and single phase. Normally no greater than 32 amps.

When on a commando socket we will install an AFDD.

If we remove the commando socket and install a standard rotary isolator, do we still need to install the AFDD ?

When to use AFDD’s for the original thread on Electricians Forums
 