B

Blunt Tool

I've spoken to Bal technical a while back when their mat first came out. Guarantee only comes into play if it's their recommended way to check and prepare sub floor, all materials must be their recommended ones. You must install as they say and must be able to provide proof! Also I was told you must lay mat with their adhesive and you must start tiling straight away so that adhesive under mat and on mat plus tile all dry at the same time like a sandwich. Was told never to stick down mat and leave till next day, only to lay what I can cover in tiles!
 
Hi everyone. I have only just seen this thread so my apologies for the delay in replying. Firstly, I would just like to say that Anhyfix has been around for several years, in that time we have installed hundreds of m2 worth of tiles successfully onto anhydrite screeds, many of them installing an uncoupling membrane, Ditra Matting, Dural CI++, Tilemaster Anti-Fracture Mat and several other systems.

Tilemaster Anhyfix does get a gradual bond to the underside of any uncoupling membrane, equally if the same test was done with a cement based adhesive, a similar thing would be seen. The bond gets stronger as time develops, and as Mark at Imperial has mentioned, try pulling the mat up after 48 hours and the results will be much different. In testing we have done here, we have applied Ditra Matting, Dural CI++ Matting and Tilemaster Anti-Fracture Matting, with C2, S1 and Anhyfix adhesives, we were extremely surprised to learn that the best bond strength we got was from Anhyfix across the board, with all three mattings that were tested.

We know that certain products are only guaranteed with a C2 or cement based tile adhesive, however for us here at Tilemaster, we know that when installing onto anhydrite/gypsum based screeds, a gypsum based tile adhesives delivers a more satisfactory result, both that the products are 100% compatible but also that we are able to deal with slightly higher moisture content that may remain within the screed.

If the manufacturer of the uncoupling membrane will not guarantee their product with Tilemaster Anhyfix, then providing the screed has been prepared correctly, Tilemaster Adhesives will offer the guarantee.
 
D

Dumbo

Just for adhesive or for everything?
TV, fridge, car ... because I'am sure the customer does. If you've shown a method statement and kept to it, then you've covered your back.
Just for adhesive and grouts. I had a job where the grout dried greyish in colour it was supposed to be limestone . I got some more of the grout mixed it up in small pots , flexible and standard they both dried a different colour to the grout in the floor and even to each other (understandable as one was flexible ) but bal said they were all in the colour parameters if I still had the pictures I would post them . So the upshot was I had to regroup the floor of my own back to keep customer happy ( I wouldn't of been happy if I was them ) with a little help from the retailer. So no I don't rely on guarantee .
 

Chris Gibbs

TF
Arms
177
608
North wales
Hi everyone. I have only just seen this thread so my apologies for the delay in replying. Firstly, I would just like to say that Anhyfix has been around for several years, in that time we have installed hundreds of m2 worth of tiles successfully onto anhydrite screeds, many of them installing an uncoupling membrane, Ditra Matting, Dural CI++, Tilemaster Anti-Fracture Mat and several other systems.

Tilemaster Anhyfix does get a gradual bond to the underside of any uncoupling membrane, equally if the same test was done with a cement based adhesive, a similar thing would be seen. The bond gets stronger as time develops, and as Mark at Imperial has mentioned, try pulling the mat up after 48 hours and the results will be much different. In testing we have done here, we have applied Ditra Matting, Dural CI++ Matting and Tilemaster Anti-Fracture Matting, with C2, S1 and Anhyfix adhesives, we were extremely surprised to learn that the best bond strength we got was from Anhyfix across the board, with all three mattings that were tested.

We know that certain products are only guaranteed with a C2 or cement based tile adhesive, however for us here at Tilemaster, we know that when installing onto anhydrite/gypsum based screeds, a gypsum based tile adhesives delivers a more satisfactory result, both that the products are 100% compatible but also that we are able to deal with slightly higher moisture content that may remain within the screed.

If the manufacturer of the uncoupling membrane will not guarantee their product with Tilemaster Anhyfix, then providing the screed has been prepared correctly, Tilemaster Adhesives will offer the guarantee.
That's very kind of you to respond, and giving the fitter peace of mind. We all care about the work we do and it's good to know we have the backing from the manufacturer too.
Thank you.
 
L

LM

Surely your leaving yourselves open to guarantee issues if you don't use one suppliers products.
schluter/Dural don't make adhesive obviously so we're forced to use a different manufacturers products. I think a bit of common sense would keep you right here. We could do a test ourselves with different mats and different adhesives on different backgrounds and try to pull up at different times/stages and trust your findings :)
 

Glynn

TF
190
473
LEYLAND
I've decided I must of had a bad bag or so of anhyfix.., tried it again from a different pile today and it was lovely, smooth, creamy and spread like a dream, pulled back the ditra and bingo... TOTAL COVERAGE!
They have batch numbers on the bags. Does anyone know how to decipher these please?

The first 6 digits of the batch number relate to the date manufactured and the last 2 digits are the batch that day. We keep a retained sample of all the batches we produce for six months so if anyone thinks there is an issue we can retest the retained sample. If anyone does feel that they have an issue with a product we take it has our duty to do a full specification test if you can give us the batch number. I was part of the team that tested Anhyfix with the de-coupling membranes and it came out top from all the adhesives we tested it with, and like Mark said it gained its bond over a couple of days.
 
L

Lodger

Zero adhesion... I'm following schluters advice and going with the ardex. Can't remember the exact one... x7 I think. I will post the primer and adhesives tomorrow.

View attachment 91756 View attachment 91757 View attachment 91758 View attachment 91759
Hi,
Looking at the anhydride screed on the picture the laytance hasn't been removed. If it's shiny then it's not scrubbed down enough.
Best way to prep the floor is to use a copper scrubbing disk or carbon stone pad on a floor cleaning machine to scarify the surface at least 1mm so you can see the poores of the screed. It should look like the edge of a plasterboard. Best to do it no longer then 1-2 weeks of screed going down or it's very deficit to scrub. The surface tends to harden over time.
Removing the laytance considerably reduces drying time.
Then use an airhydrometer available from Fball or make your own to check the floor is dry enough (85% relative humidity) before using any tiling primer 1-1 for first 2 coats then a neat coat. Primer must be dry before each coat.
If you follow these steps then you can tile straight onto the screed. No really need for decoupling mat. Not even on UFH screeds. Decoupling mat is a belt and braces approach. Use any S1-S2 type adhesive to fix tiles.
Main point is to make sure the screed is DRY.
 

Ajax123

TF
Esteemed
Arms
931
1,213
Lincolnshire
I thought you were looking for a minimum 75% rh for tiling and i have a feeling that somebody who should know ( i think it might of been @Ajax123 ) said there was no evidence to support that by removing latence you decreased drying times
Correct on both counts
 

Chris Gibbs

TF
Arms
177
608
North wales
The first 6 digits of the batch number relate to the date manufactured and the last 2 digits are the batch that day. We keep a retained sample of all the batches we produce for six months so if anyone thinks there is an issue we can retest the retained sample. If anyone does feel that they have an issue with a product we take it has our duty to do a full specification test if you can give us the batch number. I was part of the team that tested Anhyfix with the de-coupling membranes and it came out top from all the adhesives we tested it with, and like Mark said it gained its bond over a couple of days.
The bags have been burned on the fire so no way of finding out the batch numbers, although I did manage to take some photos of the problem mix against a good mix... the bad was really crumbly, weak and dull in colour against the good mix

IMG_2089.JPG IMG_2090.JPG
 
L

Lodger

I thought you were looking for a minimum 75% rh for tiling and i have a feeling that somebody who should know ( i think it might of been @Ajax123 ) said there was no evidence to support that by removing latence you decreased drying times
I think it's that kind of subfloor that people have different methods of prepping the floor.
Everyone seems to raise an eyebrow when anhydride subfloor is mentioned.
For me it's just an educated observation regarding the laytance. If you were to seal the pores of any screed holding any moisture within, then it's going to take a long time for the moisture to escape. The Laytence on anhydride screed, imho is blocked pores.
 
L

Lodger

I thought you were looking for a minimum 75% rh for tiling and i have a feeling that somebody who should know ( i think it might of been @Ajax123 ) said there was no evidence to support that by removing latence you decreased drying times
This is a quote from Bal's guide for tiling on anhydride screed

Laitance is a weak layer of fine particles deposited on the surface of the screed as the anhydrite cures. This layer is too weak to tile onto and can also inhibit drying of the screed. Many of the failures we see are as a result of contamination of the adhesive by laitance – highlighting the importance of carrying out this step.

They do also state 75% relative humidity, but Fball say it ok at 85% using their product.
 
D

Dumbo

@Ajax123 is an expert in this field as I believe he is a tech guy at a gypsum screed manufacturer therefore probably spent more time playing with these screeds than ball and bal put together . Also I haven't seen you quote anything about improved drying times apart from your own opinion . I have never fixed ceramic , porcelain or stone tiles using f.ball tile adhesives , have you ? As regards your other post maybe the floor is shiny because of the primer he has used .
 

Ajax123

TF
Esteemed
Arms
931
1,213
Lincolnshire
The ball advice is old advice. Newer information independentlybtested tells usnthag actually the licence does not significantly affect drying especially when force drying with underfloor heating.

I guess it it were blocked pores we could get some clearasil on it...
 

Reply to Anhyfix fail on ditra matting in the Canada Tile Advice area at TilersForums.com

There are similar tiling threads here

Hi everyone, I'm tiling a 150 meter square meters onto a anhydrite screed. Laitance has been...
Replies
5
Views
2K
J
Hi, I have got my kitchen extension floor to tile (6x3m). The floor is anhydrite screed which i...
2
Replies
36
Views
16K
One Day
O
T
Ok the saga begins 2 years ago with a call from a client complaining about a crunching sound...
Replies
18
Views
466
we have 80 m floor to tile which has been layed for 4 weeks now and it is a gyvlon screed type...
Replies
15
Views
11K
Mark S
M
G
So if you were using the Ditra over Anhydrite/Gyvlon type screeds what adhesive would you be...
Replies
137
Views
34K

Advertisement

Tilers Forums on FB

...
Top