As I said truly not disputing your methods or what u are saying, just keen to know. Boarding the Polypipe first before latex was a nightmare, even tho I'd marked exactly where all the pipes were on the Hardie I still stressed about clipping a pipe when it was screwed down. So being able to latex straight over would be a god send.
So the adhesive company gave u the instruction on latexing over the UFH not the UFH company itself, and u've employed this method every time? Regardless of the UFH system? I'm not digging u out! I just want to be clear how u came by the information, that's all.
Cheers.
I have to
tile onto the JG speedfit ufh system this week infact its being laid as I type...there spec sheet insists the pipework must be covered in a suitable 'floating' ply or 'floating' knauff brillo board.
I rang webber tech this morning and they said under no circumstances would they advise tiling onto a floating ply fitted over ufh and again insisted the pipes should be covered in 10mm of fibre flex leveller. I personally agree with webber on this and not the ufh manufacturer, can't get my head round tiling on floating ply..so that's the way I'm going to do the job, after levelling will be uncoupling before the tiles go down. Found this on the net...
Tiling onto under-floor heating pipes (solid substrates)
Piped heating systems are buried in reinforced
cement/sand floating screeds of not less than 65mm thick. If a polymer-modified levelling screed is used it must cover the pipes by a minimum of 10mm.
Weber's highly polymermodified adhesives and grouts have enough flexibility to accommodate thermally-induced movement.
Stage 1: Preparation
The heating pipes should be installed according to manufacturer's instructions, fixed down and tested prior to being encapsulated in a screed or levelling compound.
If the pipes have been laid in a reinforced
cement/sand screed this must be allowed to dry fully prior to tiling. A sand/
cement screed should be left for 3 weeks with the under-floor heating off to dry. After this period the heating system should be turned on and raised by a maximum of 5°C/day until the maximum recommended operating temperature is achieved. This temperature should be maintained for 3 days and then the system turned off and the screed allowed to cool to 15°C before tiling commences.
If
weber.floor flex levelling compound is used to cover the pipes instead of a
cement/sand screed, the drying time will be considerably shorter.
Ensure that the cured surface of the floor is rigid, sound, clean, dry and free from any contaminating barrier. Prime with
weber PR360 and allow to dry.